    Victory Pizza Prep Cooler

    I have been working on a Victory Pizza Prep Cooler, model: VPT-88, circa 2013.

    This cooler has been problematic from day one.

    The other day I was called in for an issue with the "rail" temperature. Upon inspection I discovered an ice ball on the compressor housing. So I went through and check the Evaporators. Defrosted the Base Evaporator with heat gun. Since the rail is cold wall, told the owner to shut the rail off for at least 12 hours. Came back the next day started up the rail. I notice that the compressor housing at the suction entry location began to ice up. I turned the rail switch off and the icing went away (melted). Turn the rail switch on again and same icing. Determined the TEV to the rail is wide open. Ordered in and changed out TEV yesterday. All went well considering it is a Victory. Started the system up and all seemed well. No compressor icing .........BUT......the dome of the compressor felt quite cold.

    I made the mistake of calling Victory/Beverage-Air Tech support this morning. I had two questions for this so called expert. (A) What is the OEM specifcation for the superheat on the Rail, and (B) what is the OEM specifications for Cut-In and Cut-out on the Rail Thermostat.

    This clown could NOT answer either question. He said the superheat was factory default---- whatever that is. I pressed him to give me a number and he wouldn't/couldn't do so. I said would this be a typical 10° TD superheat and he said that it sounded good. Moved on to the Thermostat settings. He told me that the Cut-out for the Cold Wall (Rail) was 44°. At this point I realized that a 5th Grader knew more about this cooler than this clown on the other end did.

    So, what I would like to know is the original questions:
    (A) What is the normal or typical Superheat (ie: 10°F) for the Rail Evaporator..??
    (B) What are the normal Cut-In and Cut-Out thermostat settings for the Rail..??
    HVAC/R Service Tech since 1970

  2. Likes DavidDeBord liked this post
  3. #2
    Join Date
    Jan 2010
    Posts
    13,240
    Post Likes
    Not much here ....
    Attached Images Attached Images

  4. Likes DavidDeBord liked this post
  5. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,463
    Post Likes
    Install a EPR Valve in the refrigerator section.
    Shut the rail off at night.

  6. Likes DavidDeBord liked this post
  7. #4
    Join Date
    May 2006
    Posts
    3,048
    Post Likes
    thats what happens when a company hires idots out of school who barely made it though the class and dont really want to work or learn.
    Sad isnt it

  8. #5
    Join Date
    Dec 2004
    Location
    Michigan
    Posts
    207
    Post Likes
    Thread Starter
    Just who are you calling an idiot...?? The alleged Tech Support clown...???
    HVAC/R Service Tech since 1970

  9. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,463
    Post Likes
    Quote Originally Posted by mirfgtech View Post
    Just who are you calling an idiot...?? The alleged Tech Support clown...???
    Ill guess Tech Support!

  10. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,463
    Post Likes
    Basic 8 - 10° SH is fine. Check at the pump for 20 - 40°f SH.

    EPR valve will stabilize the refrigerated section during the off cycle of the cold rail. SH at the pump should still be in range.

    What refrigerant are we dealing with?

  11. #8
    Join Date
    Jan 2010
    Posts
    13,240
    Post Likes
    R22 per manual but how's that possible with a 2010 cut off date ?

  12. #9
    Join Date
    Dec 2004
    Location
    Michigan
    Posts
    207
    Post Likes
    Thread Starter
    Refrigerant per OEM = R134A
    HVAC/R Service Tech since 1970

  13. #10
    Join Date
    Jan 2010
    Posts
    13,240
    Post Likes
    Quote Originally Posted by mirfgtech View Post
    Refrigerant per OEM = R134A
    That makes more sense then what page 27 says. Surprisingly they show R134a for the other coolers.
    What an azz outfit .

  14. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,463
    Post Likes
    1-2#’s off
    20 on