    Question WATER FLOW ISSUES ON TRANE RTAC WATER COOLED CHILLER

    A air cooled Helical Rotary liquid chiller (model RTAC 1500kw), the Chiller is not running because there is an Evaporator water Flow Status alarm issues showing ( NO FLOW) but the Flow Switch contact is closed and the pump is pumping water.. The issues here is that whenever the pump start pumping water the flow switch contact closes to alert the Chiller control module then the chiller start running but the chiller does not run,
    what could have been the issues? where in the control module is the flow switch sending signal to? is it possible the flow switch signal is not getting to the relay on the control module ?

    I need help on this issues......below is a log message




    Chiller 1 Chiller 2
    Evaporator water flow status FLOW NO FLOW
    Evaporator water pump request ON ON

    In the chiller setup, two pumps must work before the chiller starts, the issue is on chiller 2 ( NO FLOW) where there is a flow

  2. #2
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    I see your profile says you are a tech. Ask the owner if they have a Installation and Operations Manual, they should have been given one with the machine. It provides some troubleshooting guidelines. Does you machine use a digital controller (probably Yes), It is possible the sensor has gone bad. One I had Mr. B. Rabbit chewed through a flow switch sensor cable routed about 2 inches off the ground. There was really nothing wrong other than an open communication wire. Once it was replaced it worked OK again It is also possible you have flow but not enough flow to clear the logic. Unless you have some experience troubleshooting these machine it's well worth giving the local Trane service tech a call for some help as he will have the correct diagnostic software for the machine and to replace the sensor if the sensor really is bad or determine if flow is low.

    In this Open Forum that's about all I can offer

  3. #3
    Join Date
    May 2018
    Posts
    34
    Post Likes
    Thread Starter
    Thanks for your reply

  4. #4
    Join Date
    Apr 2011
    Location
    Southern Indiana
    Posts
    482
    Post Likes
    Quote Originally Posted by Joseph4blues View Post
    A air cooled Helical Rotary liquid chiller (model RTAC 1500kw), the Chiller is not running because there is an Evaporator water Flow Status alarm issues showing ( NO FLOW) but the Flow Switch contact is closed and the pump is pumping water.. The issues here is that whenever the pump start pumping water the flow switch contact closes to alert the Chiller control module then the chiller start running but the chiller does not run,
    what could have been the issues? where in the control module is the flow switch sending signal to? is it possible the flow switch signal is not getting to the relay on the control module ?

    I need help on this issues......below is a log message




    Chiller 1 Chiller 2
    Evaporator water flow status FLOW NO FLOW
    Evaporator water pump request ON ON

    In the chiller setup, two pumps must work before the chiller starts, the issue is on chiller 2 ( NO FLOW) where there is a flow
    What did you end up figuring out?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •