Results 1 to 1 of 1
Thread: CH BTU Station
    Jul 2014
    Seattle, WA
    CH BTU Station
    Finally took the time to take photos of a chiller "BTU Station" that I made last year.
    Typically you use the dP from the chiller supply & return gauges and determine the GPM from the factory chiller pressure-drop flow curve ('reflection' curve). Then you calculate Btu/hr from the dT (typically get the temps from the Chiller display panel or gauges if present).
    The only problem with this approach is that you only get spot readings - sometimes that's ok.
    My BTU station allows you to trend the data. Works pretty good. Avoid soldering your own 1/8" jacks - use the Onset gear (it's a 'jungle' out there ;-). See attached PFD.