Thread: York YCAS
    Jun 2006
    New Jersey
    York YCAS
    We in the engineering phase of re controlling a dual temp loop plant utilizing 2 York YCAS chillers. I have been trying to find out what the maximum entering water temperature that these machines can handle.
    I have reached out to York twice and no one seems to be able to get me the answer.
    The model numbers are YCAS0230EC46YGADBTXX
    montreal
    Your question is not a so easy question.
    What is the temp you're planning for at evap?
    The hard to predict condition will be outside temp.
    The problem that I see for now is if evap temp to high and outside temp is high, condensor won't be able to reject all the heat and you might trip on high pressure
    Dec 2003
    Citrus County, Florida
    Check your email
    Doug
    Jan 2013
    United Kingdom
    The highest chilled water septpoint will be around 72F, power up the panel and punch a setpoint in, so the highest temp you will be able to control leaving water temp will be around 72F, but you can PULL Down from hot water starts of 110F and the chiller will self limit on Current so as not to overload the compressors.
    Jan 2013
    United Kingdom
    It is actually 59F Max Chilled Water design temp.