    Oct 2016
    The insulation boosts efficiency in cooling also. With less insulation the suction gas gets warmer and becomes less dense. The compressor moves the same volume of gas, but less mass. So, you get a little less cooling with the higher superheat. I’d say very little difference from .5 to .75 inches of armaflex, but still different on paper.
  2. Likes baby b liked this post
  3. #15
    Apr 2018
    torrington CT
    thicker insulation is usually needed where the line is exposed to higher temperatures like outside, on a roof, or in an attic. it is also recommended that the liquid line be insulated in these areas
  4. Likes baby b liked this post
  5. #16
    May 2017
    Energy codes already require thicker insulation on linesets...just don't get enforced. Another benefit of small gains in efficiency could be seen in slightly extended system life from doing less work over time.
  6. #17
    Atlanta GA area
    Had a situation where the lineset went through a crawl (concrete floor)... suction line had 3/8 insulation on it.
    The insulation had become water-logged with sweat... and was dripping... thus adding humidity to the house.
    Removed the insulation and replaced it with 3/4, joints well taped... no more added humidity.
    Note this was in Atlanta, which has humid summers.
    GA-HVAC-Tech
  7. #18
    Jun 2002
    Dacula, GA
    For the record here Georgia uses the 2007 IECC (Energy Code) which requires a minimum of 1/2" up to 7/8" Armor Flex for the suction pipe and 1" insulation for 1" diameter pipe and over.
    In 2020 we will be using the 2015 energy code which requires R-3 insulation on all pipe below 55 F which means 3/4" minimum insulation for all pipe regardless of pipe diameter. Just a heads up. Thank you very much
    Sen. Barry Goldwater
  8. #19
    Atlanta GA area
    Any variance for colder pipes... like low temp suction lines???
    GA-HVAC-Tech
  9. #20
    Jun 2002
    Dacula, GA
    No variance for colder lines. Just everything below 40F and in 2020 below 55F. One size fits all for the minimum. Not to say you shouldn't use more insulation though. I would for super cold lines. Thank you very much