    Temps
    What are target CWS and CWR temps for a system in a resi condo, bout 150 units
    I may not be the sharpest knife in the drawer, but compared to some I'm a razor...
    Feb 2017
    New York
    Heat pumps?
    We usually run 75-80 in the summer and 70-75 in winter. Depends on the units and boiler/tower.
    -----Stop, step back, relax and have another go at it.-----
    May 2005
    Michigan
    Quote Originally Posted by BennyD View Post
    Heat pumps?
    The air handlers have a hot water coil for heating, and a separate chilled water coil for cooling. The chilled water loop temps should be ?
    May 2016
    Toronto, CAN
    44 degrees is pretty close to the normal chilled water fan coil setpoint for Leaving water temp. Doesn't really matter water entering temp is as long as is not more than 10 degs more than setpoint and your chiller can load up and down to match the load.
    May 2005
    Michigan
    Thanks for the info
    Feb 2017
    New York
    I agree. Most chilled water setpoints run from 42 to 50 depending on load and humidity levels.
    Nov 2014
    Northern Idaho
    Quote Originally Posted by gonefsihing View Post
    Leaving water temp out of the chiller barrel or the leaving water temp after its went through the coil? I think you meant the water temp entering the coil?
    May 2016
    Toronto, CAN
    I think I got it right LWT is 44. EWT is what it is as long as it's not to crazy
  9. Likes GoCougs liked this post
  10. #9
    Nov 2014
    Northern Idaho
    Leaving water temp out of evaporator or return after its went through a coil?
  11. #10
    May 2016
    Toronto, CAN
    I was referring to leaving the chiller Evap