    What are target CWS and CWR temps for a system in a resi condo, bout 150 units
    I may not be the sharpest knife in the drawer, but compared to some I'm a razor...

  2. #2
    Join Date
    Feb 2017
    Location
    New York
    Posts
    393
    Post Likes
    Heat pumps?
    We usually run 75-80 in the summer and 70-75 in winter. Depends on the units and boiler/tower.
    -----Stop, step back, relax and have another go at it.-----

  3. #3
    Join Date
    May 2005
    Location
    Michigan
    Posts
    178
    Post Likes
    Thread Starter
    Quote Originally Posted by BennyD View Post
    Heat pumps?
    We usually run 75-80 in the summer and 70-75 in winter. Depends on the units and boiler/tower.
    The air handlers have a hot water coil for heating, and a separate chilled water coil for cooling. The chilled water loop temps should be ?

  4. #4
    Join Date
    May 2016
    Location
    Toronto, CAN
    Posts
    112
    Post Likes
    44 degrees is pretty close to the normal chilled water fan coil setpoint for Leaving water temp. Doesn't really matter water entering temp is as long as is not more than 10 degs more than setpoint and your chiller can load up and down to match the load.

  5. #5
    Join Date
    May 2005
    Location
    Michigan
    Posts
    178
    Post Likes
    Thread Starter
    Thanks for the info

  6. #6
    Join Date
    Feb 2017
    Location
    New York
    Posts
    393
    Post Likes
    I agree. Most chilled water setpoints run from 42 to 50 depending on load and humidity levels.
    -----Stop, step back, relax and have another go at it.-----

  7. #7
    Join Date
    Nov 2014
    Location
    Northern Idaho
    Posts
    319
    Post Likes
    Quote Originally Posted by gonefsihing View Post
    44 degrees is pretty close to the normal chilled water fan coil setpoint for Leaving water temp. Doesn't really matter water entering temp is as long as is not more than 10 degs more than setpoint and your chiller can load up and down to match the load.
    Leaving water temp out of the chiller barrel or the leaving water temp after its went through the coil? I think you meant the water temp entering the coil?


    Sent from my iPhone using Tapatalk

  8. #8
    Join Date
    May 2016
    Location
    Toronto, CAN
    Posts
    112
    Post Likes
    I think I got it right LWT is 44. EWT is what it is as long as it's not to crazy

  9. Likes GoCougs liked this post
  10. #9
    Join Date
    Nov 2014
    Location
    Northern Idaho
    Posts
    319
    Post Likes
    Quote Originally Posted by gonefsihing View Post
    I think I got it right LWT is 44. EWT is what it is as long as it's not to crazy
    Leaving water temp out of evaporator or return after its went through a coil?


    Sent from my iPhone using Tapatalk

  11. #10
    Join Date
    May 2016
    Location
    Toronto, CAN
    Posts
    112
    Post Likes
    I was referring to leaving the chiller Evap