    407c??

    Green tech guy.
    Supply company telling me you can add this on top of r-22, but most techs say it's a retrofit, any suggestions?


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,900
    Post Likes
    Can be added with no TXV adjustment.

    Here is another post that looks into this further.

    http://hvac-talk.com/vbb/showthread....g-407C-and-R22
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  3. Likes Jettinvr6sc, weezer81 liked this post.
  4. #3
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Positively not! You seem to be saying that you will mix the refrigerants.
    The old refrigerant must be recovered and replaced with the new refrigerant.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  5. Likes Gunslinger, weezer81 liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •