comparison with vav box vs vav box with reheat
i need comparison with vav box & vav box with reheat
advantage & disadvantage
cost
thanks
What are you going to do with a comparison? You need the reheat or you don't. If cost is that important don't build.
Post Likes - 1 Likes, 0 Dislikes
Reheat so you don't overcook the space, VAVs have a minimum position @ minimum, typically reheat is energized...where I am, the VAVs with reheat are typically on the perimeter of the building, while the core has regular VAV
If the load is calculated properly you can use just VAV boxes but some one will always complain about temperature. Without reheat the heating load is handled by the load in the space such as lights, computers, people and/or reheat on perimeter boxes. etc. With reheat you get the ability to have faster temperature change and in my opinion more precise control over temperature. Plus the added benefit of changes in the building in the future in case you lose heating load due to occupancy decreasing etc. I believe VAV with reheat is the most energy efficient if done with hot water for the building.
Disaadvantages of Reheat boxes is cost to install hot water or steam piping or electric reheat. Electric reheat is not as efficient.
To reheat or not to reheat that is the question.
Originally Posted by
browntg
Electric heat is 100% efficient
lkapigian
And 100% expensive lol
electric heat rules if your a cheap slumlord.
jbhenergy
Agreed, but don't confuse efficiency VS cost...oputput/input
Depends on where you live in my state in the 70s it was used over any other type of heat as electric was DIRT CHEAP back then.
Now its gas oil propane then geo
jbhenergy
Depends where your at. Some places it is the cheapest option
UA Proud
"Phfft! Facts. You can use them to prove anything." Homer Simpson
Depends on the system supplying the box and the type of space its being used in. An interior section of an office probably isn't necessary. If you're in an exterior zone with several windows IMO reheat would be a good choice.