    Manitowoc Indigo Starving TXV Fault

    Hello guys, one of the many ice machines at the casino I work at has been getting a starving txv fault every time it makes ice..but that's what is weird, it seems to not be having any problems at all making ice. I looked at the thermistors and the inlet temp is in normal ranges but the outlet temp is around 130 degrees at all times!! So is this something I need to call service on asap or is something possibly just wrong with the thermistor? In the manual it says the thermistor is shorted at 475 degrees and open at -22 degrees though so I'm assuming it is working properly. I will try to check it manually tomorrow, its in a difficult place. Also, on a couple of my ice machines I noticed during harvest the evaporator outlet temp is the same as the inlet. I figured the temp would drop by the time it got to the outlet. Sorry if these questions are stupid, I'm just a 22 year old maintenance tech with much to learn lol.

  2. Likes UmmScott liked this post
  3. #2
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    557
    Post Likes
    Hey, I am a 20 year old maintenance engineer with lots to learn too! Maybe I Can help.

    First of all, Does the ice machine actually say that it has a starving TXV fault? That would indicate a leak, never heard of anything monitoring that on a system but hey, maybe its new.

    IF the TXV was starving, it wouldn't be able to feed the evaporator properly in which case you wouldn't really be making ice without problems. It could also be the sensing bulb from the TXV fell off or something and its actually overfeeding the coil but because the bulb is in the wrong place, it thinks its starving as its not getting any colder where the bulb is.

    I am just guessing here, I am sure some of the more experienced techs will pipe in.

    Okay, so I checked online, turns out it does tell you.
    https://icemakerpartsshop.com/blogs/...-trouble-codes

    Its either TXV fault or low charge so the above should apply to you.

  4. #3
    Join Date
    Jan 2017
    Location
    KS
    Posts
    8
    Post Likes
    Thread Starter
    Thanks for the reply! I will have to check the sensing bulb tomorrow when I manually check the outlet temp. But yeah, I figured if I was getting a txv fault and the machine wasn't freezing properly then that would make sense but it is actually working just fine. I just didn't know if it is something that might start to crap out over time.

  5. #4
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    14,333
    Post Likes
    Don't mess with the txv bulb.

    If it's making ice there is NO WAY you have 130° at the evap outlet.

    It's a bad Thermistor

    You can swap two Thermistors to verify the board and connections but it's a bad Thermistor.

  6. Likes UmmScott liked this post
  7. #5
    Join Date
    Nov 2006
    Location
    Wisconsin
    Posts
    482
    Post Likes
    Quote Originally Posted by itsiceman View Post
    Don't mess with the txv bulb.

    If it's making ice there is NO WAY you have 130° at the evap outlet.

    It's a bad Thermistor

    You can swap two Thermistors to verify the board and connections but it's a bad Thermistor.
    Ditto. These thermistors are notorious for going bad. I have changed quite a few. It would be an easy repair for you to do. The kit comes with a universal thermistor, and stickers to label it, and mounting clips.
    You have to remove the insulation, remove the thermistor and clip. Install and label new thermistor, reinstate, done.

  8. Likes UmmScott, brettross94 liked this post
  9. #6
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    2,853
    Post Likes
    Bad thermistor..as others stated.
    Not a refrigeration problem in any way.

    Sent from my SM-N920V using Tapatalk

  10. #7
    Join Date
    Jan 2017
    Location
    KS
    Posts
    8
    Post Likes
    Thread Starter
    Thanks guys. I took the thermistor off this morning and ohmed it and sure enough its no good. Got a new one on order. Its good to know that it can still be bad even if its not shorted.

  11. Likes UmmScott liked this post
  12. #8
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    2,853
    Post Likes
    Quote Originally Posted by brettross94 View Post
    Thanks guys. I took the thermistor off this morning and ohmed it and sure enough its no good. Got a new one on order. Its good to know that it can still be bad even if its not shorted.
    Good job man.

    Yeah they can be really really weird.
    I had a traulsen cooler that the sensor would read fine above 39.

    But once the temp dropped below 39, thats all the further the sensor would register.
    So the box would continue to cool down to like 25F and still be reading 39F LOL

    Sent from my SM-N920V using Tapatalk