    Duct dampers or just partially close registers?

    Hi,
    I have several floor registers that are really blowing air and I am keeping them partially closed. Is it better for the distribution system to put dampers in the ducts near the main plenum or does it not matter?
    Gary

  2. #2
    Join Date
    Jun 2005
    Location
    The Gray Northwest
    Posts
    661
    Best to install a balancing damper at the branch where it exits the main trunk.

  3. #3
    Join Date
    Nov 2008
    Location
    Chapel Hill, NC
    Posts
    1,053
    Partially (or more) closing the register will produce wind noise. Closing the dampers at the branch will do the same at the damper but it won't be as audible in the room. As to whether it makes any difference to the performance/reliability of the system as a whole, I'll let someone more experienced answer that.

  4. #4
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Quote Originally Posted by sktn77a View Post
    Partially (or more) closing the register will produce wind noise. Closing the dampers at the branch will do the same at the damper but it won't be as audible in the room. As to whether it makes any difference to the performance/reliability of the system as a whole, I'll let someone more experienced answer that.
    Makes no difference except as noted above.


    However closing register or duct dampers too much canraise the static
    (resistance to air flow) too high and damage the equipment.The better the duct system was designed and installed the better you will be able to balance it with either method.

  5. #5
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,338
    Audible noise around a round butterfly valve (assuming we're talking about round supply ducts), should produce much less noise than the flaps on a register.

    Also restricting flow at the register can increase loss at any leaks on that supply branch. Using a damper upstream essentially creates a pressure drop across it.

    Balancing issues from inadequately sized branches or trunks can definitely be a problem. Imbalance because of too little size reduction at the end of the main trunk, would increase static, but shouldn't cause any problems.