Page 3 of 4 FirstFirst 1234 LastLast
Results 27 to 39 of 41
  1. #27
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,421
    Post Likes
    Thread Starter
    Economizers have been disabled and linkage adjusted to close dampers as tightly as possible.


    Quote Originally Posted by Juan Madera View Post
    So, if you are looking up at the underside of the roof, you can see the unit's curb? If not and there is ducting above the hard ceiling, the RA duct might have been compromised perhaps. If you can see the curb and all the ducting and know that it is intact, the economizer might need some judicious application of some mastic to the damper blades after you de energise the actuator motor... That is provided that you don't need OA for the server room. Easy relief damper is a bit of rubber belting zip screwed at the top over an appropriately sized hole in the SA on the unit... Still amazed that a unit this large and having an economizer does not have a relief damper in it already. Most of my big RTU's have interlocked linkage that work the OA and relief at the same time.

  2. #28
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,421
    Post Likes
    Thread Starter
    With roughly 48,000 CFM on a roughly 2,000 square foot room, I'm pretty sure there will be plenty of fresh air due to leakage.


    Quote Originally Posted by hvacker View Post
    Just to add, a closed damper will still leak. Sometimes a lot depending on the type. Leakage of 10% isn't uncommon. This can be tested using the temperature method if necessary.

  3. #29
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    1,223
    Post Likes
    Some server rooms have outside air and some do not. The ones that do usually have just enough OA to slightly pressure the space. Fresh air requirement isn't much of an issue because most are only occasionally occupied. Economizing is not normally done.
    I have never seen a server room supported by one large AHU. If that is what you have there is no redundancy which is normally a major design consideration.

  4. #30
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,421
    Post Likes
    Thread Starter
    For the last of the three photo's, I'm standing on top of the second unit.

    120 tons of A/C for 2,000 square feet.

  5. Likes stanbyyourword liked this post
  6. #31
    Join Date
    Feb 2017
    Location
    New York
    Posts
    656
    Post Likes
    Makes sense. With a return restriction due to the lack of return grills, the unit was seeing a good negative return pressure. This would make the unit pull even more air through the OA dampers.

    I've had a similar issue on some 15 ton units. I used sheet metal and foam tape to make a tight seal against the damper when it was fully closed. Did help.
    -----Stop, step back, relax and have another go at it.-----

  7. #32
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    7,833
    Post Likes
    Saw the pictures. What a crappy job. Isn't exposed duct required to be insulated in CA?
    There is so much outside duct an access should be cut so the duct can be sealed from the inside unless the existing sealant is better than it looks.
    I expect ducts to leak 10% or more on older installs. Duct pressure testing can be a real eye opener for those that think sheet metal joints are air tight.

    I've seen exposed glue lams for architectural details and I've had a piece outside for 15 years or so and it's surviving so far. That doesn't mean it's approved. It would still seem to need a preservative I would think. Maybe it has one. All the good preservatives have been pulled from the market thanks to CA. Stuff like Penta preservative is missed.


    Hopefully you won't need to go to this extreme but with 120 tons on 2000 sq ft you might. On one space I had with oversized equipment that resembled a wind tunnel I disabled one of two compressors, blocked half the evap coil and slowed the fan to match the new capacity. Like said...extreme.

    A server room really doesn't want uncontrolled infiltration with all the crap blowing around.
    Blocking off the OSA dampers and doing any necessary duct sealing and insulating. Adding a damper for any OSA necessary. You still might need to cut capacity because of short cycling.
    Or your sales person might make a call to replace the whole mess with a couple of rational replacement units. Operating costs won't get cheaper.
    I should have played the g'tar on the MTV. MK

    You can be anything you want......As long as you don't suck at it.

    SMW Lu49

  8. #33
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,421
    Post Likes
    Thread Starter
    Normal around here to insulate the exterior ducting on the interior of the duct. Didn't really inspect for that, but pretty sure it's insulated, I remember looking up into the return when I was in the room. Think I would've noticed if I was looking at sheet metal.

    But yeah, pretty crappy install. Those ducts span something like eight feet. Unsupported. And with metal too thin. You need a real tall standing seam, supports inside the ducting, or external supports. The duct sealant applied to the exterior is so thin it didn't even do its job.

    Since the tenant is just taking occupancy, seriously doubt they're going to be re-doing anything in the near future.

    For now, they're happy they can open the door much more easily.


    Quote Originally Posted by hvacker View Post
    Saw the pictures. What a crappy job. Isn't exposed duct required to be insulated in CA?
    There is so much outside duct an access should be cut so the duct can be sealed from the inside unless the existing sealant is better than it looks.
    I expect ducts to leak 10% or more on older installs. Duct pressure testing can be a real eye opener for those that think sheet metal joints are air tight.

    I've seen exposed glue lams for architectural details and I've had a piece outside for 15 years or so and it's surviving so far. That doesn't mean it's approved. It would still seem to need a preservative I would think. Maybe it has one. All the good preservatives have been pulled from the market thanks to CA. Stuff like Penta preservative is missed.


    Hopefully you won't need to go to this extreme but with 120 tons on 2000 sq ft you might. On one space I had with oversized equipment that resembled a wind tunnel I disabled one of two compressors, blocked half the evap coil and slowed the fan to match the new capacity. Like said...extreme.

    A server room really doesn't want uncontrolled infiltration with all the crap blowing around.
    Blocking off the OSA dampers and doing any necessary duct sealing and insulating. Adding a damper for any OSA necessary. You still might need to cut capacity because of short cycling.
    Or your sales person might make a call to replace the whole mess with a couple of rational replacement units. Operating costs won't get cheaper.

  9. #34
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    7,833
    Post Likes
    The stuff inside is probably just sound deadening material. The black bats glued to the metal. It has some minor insulating qualities but that's not what it's for. It's to quiet air noise.
    If I remember it's usually 1" r1 or r2. With that much metal exposed the skin transfer will be high. I used to have some charts giving the loss/gain but their misplaced.
    My guess is no permit was pulled.
    I should have played the g'tar on the MTV. MK

    You can be anything you want......As long as you don't suck at it.

    SMW Lu49

  10. #35
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,421
    Post Likes
    Thread Starter
    I didn't think I needed to ask. The install speaks for itself.


    Quote Originally Posted by hvacker View Post
    The stuff inside is probably just sound deadening material. The black bats glued to the metal. It has some minor insulating qualities but that's not what it's for. It's to quiet air noise.
    If I remember it's usually 1" r1 or r2. With that much metal exposed the skin transfer will be high. I used to have some charts giving the loss/gain but their misplaced.
    My guess is no permit was pulled.

  11. #36
    Join Date
    Apr 2015
    Posts
    3
    Post Likes
    If you look at it terms of air changes you could have as much as 1440 ACH of supply air in the space. If you only had 2% leakage that would still be about 29 ACH of outside air. To put that into perspective, operating rooms requires a minimum 20 ACH and 4 ACH of outside air. In fact, your ACH is acutally higher in theory because the servers might take up a significant amount of volume in the space.

    The solution: Either re-evaluate the need for (2) 60 ton units or add an exhaust fan.

  12. #37
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,421
    Post Likes
    Thread Starter
    Tightly closing the outside air dampers has greatly improved the situation.


    Quote Originally Posted by Redhau5 View Post
    If you look at it terms of air changes you could have as much as 1440 ACH of supply air in the space. If you only had 2% leakage that would still be about 29 ACH of outside air. To put that into perspective, operating rooms requires a minimum 20 ACH and 4 ACH of outside air. In fact, your ACH is acutally higher in theory because the servers might take up a significant amount of volume in the space.

    The solution: Either re-evaluate the need for (2) 60 ton units or add an exhaust fan.

  13. #38
    Join Date
    Sep 2002
    Posts
    21,602
    Post Likes
    Huh; so you were adding something to the space all along, eh? <g>

    I might gasket some sheet metal over the OA intake.

    I guess now you'll want to start checking that return duct leak rate. <g>

    PHM
    --------




    Quote Originally Posted by BBeerme View Post
    Tightly closing the outside air dampers has greatly improved the situation.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  14. #39
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,421
    Post Likes
    Thread Starter
    I think if you will re-read the third paragraph in the very first post on this thread, that is what I said.

    To eliminate further high static in the room, they need more return grills for the common attic return.

    Since the people there were convinced it was a balance issue, I popped a bunch of ceiling tiles to check for dampers. I didn't unwrap any insulation, just pressed on it trying to feel for the damper handles. But I left all of the ceiling tiles out as I went.

    When I was done, I checked for static at the door. Since this is the barometer that everyone was using. And virtually no static. Teeny tiny bit, yes. But the door opened and closed normal.

    Remember, in the second paragraph in the very first post on this thread, I mentioned that small people there could not even open the door. That's how bad the problem was.


    All that said, yup, next time it rains, the return will likely suck in water. There is little doubt there.


    Quote Originally Posted by Poodle Head Mikey View Post
    Huh; so you were adding something to the space all along, eh? <g>

    I might gasket some sheet metal over the OA intake.

    I guess now you'll want to start checking that return duct leak rate. <g>

    PHM
    --------