Results 1 to 11 of 11
  1. #1
    Join Date
    Jan 2006
    Location
    Hamilton Ontario Canada
    Posts
    1,413
    Post Likes

    Digital Manometer

    Here is one for you. Another tech calls me at home the other night and tells me my manometer is screwed up. He was out on a call that I had done the set up on. Low fire 1.9wc high fire 3.5wc. He tells me my manometer is not working right because he hooked up his and the high fire was 2.8wc so he brought it up to 3.5wc and told the customer that everything was fine now that the gas pressure was set right.
    I grab my Dwyer u tube off the truck and hook it up to my furnace and check where it is sitting. 1"3/4 down and 1"3/4 up good 3.5wc. Hook my Testo 506 up and 3.53wc. Guess who has the screwed up manometer and has to go back to the over fired furnace. He is using a UEI manometer I told him at the shop the next morning he better get a new manometer. He then tells me there must be alot of furnaces out there that he has overfired.

  2. #2
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,405
    Post Likes
    I just bought a Testo 510 about a month ago. First digital I ever bought. Checked it against my magnahelic, dead on. Last week I was a pharma lab, which has the lab pressure calibrated monthly. Pulled the hose off there magnahelic and hooked it up to my Testo, was off about 0.1". I'm happy with that.

  3. #3
    Join Date
    Jan 2006
    Location
    Hamilton Ontario Canada
    Posts
    1,413
    Post Likes
    Thread Starter
    Until I checked my Testo against the Dwyer u tube. I felt ok using the Testo 506. That was the first time I had doubts about my digital manometer. I think I will check it more often against the u-tube.

  4. #4
    Join Date
    Mar 2008
    Posts
    624
    Post Likes
    i bought the 510 aswell. not disappointed. also .1 is a bit high, you sure it wasnt .o1? i use mine for static pressures and if im off by .1 then im in trouble!
    HVAC PRO IN THE MAKING
    NATE's:
    Gas Heat Service/ Installation
    Air-to-Air Heat Pump Service/ Installation
    Air Conditioning Service/ Installation

  5. #5
    Join Date
    Mar 2001
    Posts
    1,213
    Post Likes
    I check my UEI with a U-tube on a reg. basis..... So far it's good.

  6. #6
    Join Date
    Mar 2008
    Location
    Breslau, Ontario
    Posts
    521
    Post Likes
    digital tpi 620 works very well confident in the results

  7. #7
    Join Date
    Apr 2008
    Location
    OKC, OK
    Posts
    10
    Post Likes
    I use a fluke 922, and magnahelic's 0-1.0"W.C. and 0-2.0"W.C.
    Both work fine for me.

  8. #8
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,405
    Post Likes
    Quote Originally Posted by Profiler View Post
    i bought the 510 aswell. not disappointed. also .1 is a bit high, you sure it wasnt .o1? i use mine for static pressures and if im off by .1 then im in trouble!
    It was 0.01" wc. Sorry for my bad typing.

  9. #9
    Join Date
    Nov 2003
    Location
    Montreal, Qc.
    Posts
    834
    Post Likes
    My company supplied me with a UEI which I double check with my slant tube manometer.
    So far it's accuracy is within 0.01" w.c.
    If I were to purchase one myself it would be the Fluke.
    Now I need to find surgical grade silicone tubing that won't get hard in the freezing cold.

  10. #10
    Join Date
    Apr 2008
    Location
    Central CA
    Posts
    567
    Post Likes
    Thump here is what i use

    Pure Silicone Tubing Shape Single Line Maximum Pressure Range, Under 100 psi Low Temperature Range -99 to -1 F High Temperature Range +301 to +500 F Fittings Used Barbed 1/8" ID x 1/4" OD wall Specifications Met United States Food and Drug Administration (FDA)

    http://www.trutechtools.com/cart/ind...ort=20a&page=2

  11. #11
    Join Date
    Nov 2003
    Location
    Montreal, Qc.
    Posts
    834
    Post Likes
    Quote Originally Posted by stomper56 View Post
    Thump here is what i use

    Pure Silicone Tubing Shape Single Line Maximum Pressure Range, Under 100 psi Low Temperature Range -99 to -1 F High Temperature Range +301 to +500 F Fittings Used Barbed 1/8" ID x 1/4" OD wall Specifications Met United States Food and Drug Administration (FDA)

    http://www.trutechtools.com/cart/ind...ort=20a&page=2
    Thank You,

    That's exactly what I'm looking for.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.