    One programmable Honeywell t-stat will stop calling for heat 2*F below the set point........... then after a few minutes, kick the furnace back on for the last 2*F until the T-stat is satisfied. Only happens on cycles that require a larger rise in temperature. I don't remember which model this occurs with.

  2. #22
    Join Date
    Jan 2007
    Location
    Connecticut
    Posts
    47
    Post Likes
    Thread Starter
    Quote Originally Posted by t527ed View Post
    what type of thermostat?

    is whole unit shutting down like a normal cycle or does blower keep running?

    on a big recovery thermostat could be cycling furnace so it does not overshoot temp setting.
    follow up....

    I came home from work today.
    Wife had already turned up the thermostat to the usual 68 degrees. She said the temperature on the thermostat when she came home read 62 degrees. (I turned the thermostat down to 55 degrees when I left the hose this morning).
    I checked the thermostat. It read 66 degrees.
    I ran downstairs to check the furnace.
    It was off. completely off.....no blower....no nothing....and it hadn't yet reached the 68 degrees setting.
    It kicked back on a few minutes later and then went to 68 degrees.

    SO.....the furnace couldn't go from 62 degrees to 68 degrees without shutting down at least once.

    so.....since everyone says this is not proper operation (that is, the furnace should run constantly until it reaches the set temperature), I will be calling the installer tomorrow.

    i'll keep you posted.

    UGH!

  3. #23
    Join Date
    May 2004
    Location
    Fayetteville TN
    Posts
    656
    Post Likes
    Anticipator/cycle rate?
    If You don't have time to do it right, when will you have the time to do it over?

    "Perception is Reality" Look & Act like a Professional

  4. #24
    Join Date
    Jan 2007
    Location
    Connecticut
    Posts
    47
    Post Likes
    Thread Starter
    Well, I am gonna try and change the thermostat to see if that is the problem....

    but, even that is not a simple job.

    that saga is detailed here:

    http://hvac-talk.com/vbb/showthread.php?t=234312

    ugh.

  5. #25
    Join Date
    Jan 2007
    Location
    Connecticut
    Posts
    47
    Post Likes
    Thread Starter
    I installed a new thermostat (Honeywell Focus Pro 600 #TH6110D1005) last night, but before I did I ran the furnace on the old Honeywell stat to see what happened...

    Here's what happened:

    Got home.
    Stat read 63 degree house temp.
    Set the heat at 73 degrees and furnace fired up.
    Took about 9 minutes to get to 64 degrees.
    Approximately 20 minutes later, with the temp at 66 degrees, furnace shut off.
    Blower ran for approximately 2:30 then the furnace was completely off.
    Furnace fired up approximately 2 minutes later.
    Furnace ran for approximately 29 minutes then turned off. Temp was 71 degrees.
    Blower ran for approximately 2 minutes then furnace was completely off.
    Furnace fired up about 1 minute 15 seconds later.
    Furnace ran for approximately 10 minutes and then turned off. Temp at 71 degrees.
    Blower ran for approximately 2 mim 30 seconds then furnace was completely off.
    Furnace fired back up approximately 1 minute later.
    73 degrees obtained some time later. (lost track of how long it ran to get from 71 degrees to 73.)

    Each time the furnace shut down, I went downstairs and checked the peephole on the furnace to see if the little red light was blinking any codes. It wasn't.

    So I then changed the stat and hopefully that will fix it. If not, then the installer will be coming out.

    anyone have any thoughts on my problem??

    thanks.
    mike

  6. #26
    Join Date
    Jan 2007
    Location
    central america
    Posts
    157
    Post Likes

    Hmm

    Quote Originally Posted by superheatrman View Post
    Mrmjmoore,
    your filter is making the temperature rise thru the heat exchanger higher. to high for the furnace to stay on, your are reaching the high limit when the furnace shuts down the burner, and the blower continues to run to cool it. when the limit cools the furnaces restarts the heating cycle. this is the stopping and starting you hear. this will eventually wear out alot of parts prematurely. A cheap filter{fiberglass} will help, but not fix this issue. Most cases require increasing the blower speed and lowering the gas pressure to the burnners. to lower the overall heat input. temperature rise is how you determine how much you need to lower the gas pressure to meet your air flow, with your endust{very restrictive} filter in place. You need to take accurate supply and return temps, find the temp rise rating on manufactures rating plate. make, model numbers , pics of furnace and ductwork. are also helpful...
    can you see the diagnostic light at all?

  7. #27
    Join Date
    Jan 2007
    Location
    Connecticut
    Posts
    47
    Post Likes
    Thread Starter
    Well, it seems to have been a thermostat problem, as my installer thought it was.

    With his help, I installed a new thermostat.
    Installed a Honeywell Focus Pro 6000 (TH6110D1005).

    Since installing the thermostat, the furnace has run continuously until it reaches the set temperature.
    Most times it has been from about 62 degrees to 68 degrees......runs non stop, no problems.
    But I finally went a away for a weekend and gave the house a chance to cool down to 55 degrees.
    Set the temp to 68 degrees when I got home and the furnace ran non-stop until it reached 68 degrees. Took the furnace about 45 minutes or so.

    Problem solved. Excellent.
    Thanks to everyone who helped.

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •