    Quote Originally Posted by technocratic View Post
    Your tech should be able to quickly figure it out by reading the schematic of the unit. Usually I pump them down and then recover whats left. Pulling a vacuum with a compressor can damage the motor.

    Sent from my SM-G935T using Tapatalk
    Yeah because when he moves it to the other side of the house it is very unlikely it will have the exact same length of lines. So you would have to charge it according to the new location.


    Sent from my iPhone using Tapatalk

  2. #15
    Join Date
    Nov 2012
    Posts
    10
    Post Likes
    Thread Starter
    I guess I should have mentioned that I'm closing down the high pressure service valve and because this is a heat pump I had to jumper the reversing valve wire to put the system in cooling mode.

  3. #16
    Join Date
    Aug 2013
    Location
    Visalia California 93291
    Posts
    7,337
    Post Likes
    How far is the condensing unit to the air handler now

  4. #17
    Join Date
    Jun 2016
    Posts
    145
    Post Likes
    Quote Originally Posted by cahhtravis4 View Post
    I guess I should have mentioned that I'm closing down the high pressure service valve and because this is a heat pump I had to jumper the reversing valve wire to put the system in cooling mode.
    Why are you jumpering the unit to put it in AC mode? I would go to the thermostat and put it on cool. Just recover the extra and adjust to new location. R410 is cheap.


    Sent from my iPhone using Tapatalk

  5. #18
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,116
    Post Likes
    Quote Originally Posted by pecmsg View Post
    So what does your tech say?
    Still waiting for a answer!

  6. Likes kdean1 liked this post
  7. #19
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    4,928
    Post Likes
    Quote Originally Posted by lkapigian View Post
    It look like your past posts show you have some technical background, I would try and move this to Tech to Tech, still an open forum but you may get more answers
    But don't start another thread with the same name and topic.
    OOPS! Too late.
    AOP Rules: Rules For Equipment Owners.

    Free online load calculator: http://www.loadcalc.net/


    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."

  8. #20
    Join Date
    Nov 2012
    Posts
    10
    Post Likes
    Thread Starter
    My tech is the old school type and he thinks that this could be a scroll type compressor with a pressure bleed off that wont allow the pressure to drop below 50 psi to protect the compressor.

  9. #21
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    6,654
    Post Likes
    I'm very confused about the way this went down.

    Tech came out to your house.
    Pumps back unit.
    Comes to you and says "unit won't pump down below 50psi".

    and then....leaves? Tells you to go online for the answer?


    How the heck did you get from there, to here?
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  10. Likes mnbvcxz liked this post
  11. #22
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    6,654
    Post Likes
    I'm very confused about the way this went down.

    Tech came out to your house.
    Pumps back unit.
    Comes to you and says "unit won't pump down below 50psi".

    and then....leaves? Tells you to go online for the answer?


    How the heck did you get from there, to here?
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  12. Likes mgenius33 liked this post
  13. #23
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,853
    Post Likes
    Merged threads.

    As far as I can tell, you are not a tech, so please don't start any threads in the Tech to Tech forums.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?