    Ok, let me see if in can spot all the issues here
    1) wrong pitch on venting
    2) metal tape on flue
    3) no visible fasteners between single wall and b-vent elbow (glossing over the fact that they used an elbow as an extension piece coming off the inducer)
    4) no support for the vent (except for the circulator)
    5) serviceability of the circulator
    6) serviceability of the expansion tank
    7) flex gas pipe creates a trap,
    8) I may be wrong, but i dont think that yellow wire is supposed to be used, it should be BX or MC
    9) exposed wiring in a junction box
    10) unsecured junction box
    11) unsecured switch
    12) may not be code here but shouldn't that switch be red and say gas unit emergency shutoff?
    13) also may not be code here, but there should be an electrical fusible link?
    14) leaking hi-vent
    15) shouldn't that stub nipple next to the circ have a hi-vent instead of a cap
    16) no downpipe on the relief valve
    17) that gas pipe seems to have been reduced quite a lot.
    18) zip tie bandit was here, stole all the ties out of the unit and left the wires a mess
    19) nothing seems to be level or plumb, and they must have gotten paid by the fitting
    20) looks like every fitting has leaked at least once
    Bonus points: 1 single piece of armaflex on the valve, and it looks like it was the wrong size to begin with.
    thats all i can spot. let me know if i missed any
    The "F" on the blue crown boiler panel in the left of the photos should be moved to the front panel of this unit.....
    The bible is my constitution and the constitution is my bible.
    WE THE PEOPLE refers to THEM and not YOU.
    Chewbacca Mom 2016
  6. #31
    Nothing Wrong with the 70's i grew up in that generation
    Was fun we had a l lot of fun
  7. #32
    The picture you posted looks more like a set for a tv show of that era though
  8. #33
    Dec 2011
    hartford ct
    Cool
    Quote Originally Posted by n-e-w Jerz! View Post
    You pretty much nailed it, you win this BRAND NEW CAAAAAARRRR!
    if it looks anything like that boiler, i dont want it.
  9. #34
    Mar 2017
    wow
  10. #35
    Aug 2012
    good thing they left the paperwork
  11. #36
    Cincinnati, Oh
    Quote Originally Posted by burnermanriz View Post
    Boiler is piped backwards
    Sent from my iPad using Tapatalk
    Actually, it's pipe correctly. Believe it or not.
    That pump is designed to be on the outlet of the boiler, and it's pumping away.
    I mean, the rest is horrible, but just an FYI, that's where they put the pump.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."
    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
    "Just get it done son."
    Dad adjusted
  12. #37
    Jun 2016
    Plano, TX
    14) leaking hi-vent
    Flex pipe into the boiler. Should be hard pipe through the boiler jacket. If it's got an induced draft motor, you can pitch the vent down... in certain applications.
    Wir kontrollieren Feuer und Eis