    clogged cap or low on gas?

    whats the easiest way to determine if residential frig has filter or cap clogged or low on gas from leak?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    12,957
    Post Likes
    Start with Pull the charge and weigh it, move on from there.

  3. Likes UmmScott liked this post
  4. #3
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,409
    Post Likes
    System should equalise pressure when switched off. If stays in a vacuum cap is plugged.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  5. #4
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,541
    Post Likes
    Residential? Just buy a new one.
    Local 449?

  6. Likes ga-hvac-tech, UmmScott liked this post
  7. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,359
    Post Likes
    If a residentail frig has electrical problem, fix it, but when its got refrig problem, dont waste your time

  8. Likes Juan Madera, UmmScott liked this post
  9. #6
    Join Date
    Aug 2013
    Posts
    34
    Post Likes
    I have a similar question with a Sub Zero under counter refrigerator. Going to dig deeper into it tomorrow but I did notice on visual inspection today the cap tube had frost starting about 6 inches from the evap coil. I'm a residential tech and I'm tinkering so any info on cap tube restrictions would be great. Would ice before the evap coil be a guaranteed restriction or could other issues cause that?

  10. #7
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    7,614
    Post Likes
    A restriction will be accompanied with a temperature drop at the point of restriction.
    If a drier for example feels normal on one end but cold or frosting on the other it's restricted.
    Usually a cap tube restriction will be on just one tube. If they all are plugged look at the distributor before the tubes. Some have a strainer there.
    Frost=pressure drop.
    Ice usually indicates the evap is too cold because it can't transfer to the load. Dirty coil, fan problem if there is one etc.
    Frosting back to the compressor, look at the charge. A restriction usually won't have the refrigerant capacity to frost much beyond the restriction.
    I know this is fairly general but frost is one thing and ice is another.
    I should have played the g'tar on the MTV. MK

    You can be anything you want......As long as you don't suck at it.

    SMW Lu49

  11. #8
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    15,613
    Post Likes
    Quote Originally Posted by targetman View Post
    Residential? Just buy a new one.
    Quote Originally Posted by Snapperhead View Post
    If a residentail frig has electrical problem, fix it, but when its got refrig problem, dont waste your time
    One caveat. If it's your own frig, you got the time, and have that burning desire to figure things out, then you play to your hearts content.

  12. #9
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    15,613
    Post Likes
    We're talking residential frig.

    Most of those things you mentioned don't apply.

    Like when they run the cap tube inside the suction line.

    Or solder the cap tube to the suction line.

    Or you can't even see half of the cap tube due to the construction of the box.



    Quote Originally Posted by hvacker View Post
    A restriction will be accompanied with a temperature drop at the point of restriction.
    If a drier for example feels normal on one end but cold or frosting on the other it's restricted.
    Usually a cap tube restriction will be on just one tube. If they all are plugged look at the distributor before the tubes. Some have a strainer there.
    Frost=pressure drop.
    Ice usually indicates the evap is too cold because it can't transfer to the load. Dirty coil, fan problem if there is one etc.
    Frosting back to the compressor, look at the charge. A restriction usually won't have the refrigerant capacity to frost much beyond the restriction.
    I know this is fairly general but frost is one thing and ice is another.

  13. #10
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    15,613
    Post Likes
    I'm going with Pecmsg on this one.

    But I would be curious what the suction pressure and subcooling is if after weighing it in. Especially if that doesn't get it to cool.


    Quote Originally Posted by pecmsg View Post
    Start with Pull the charge and weigh it, move on from there.

  14. #11
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    7,614
    Post Likes
    Quote Originally Posted by BBeerme View Post
    We're talking residential frig.

    Most of those things you mentioned don't apply.

    Like when they run the cap tube inside the suction line.




    Or solder the cap tube to the suction line.

    Or you can't even see half of the cap tube due to the construction of the box.

    That's why I said "Fairly general" All this applies when it can apply.
    I believe the difference between ice and frost needs to be understood because the ?? comes up a lot.
    I should have played the g'tar on the MTV. MK

    You can be anything you want......As long as you don't suck at it.

    SMW Lu49

  15. #12
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,416
    Post Likes
    A unit low on charge will usually frost up the cap tube a few inches before the evaporator JUST LIKE a restriction. Anybody thinking they can tell the difference visually will be as luck as flipping a coin. Might be right might not.

    How quickly pressures equalize is also an incredibly poorly unreliable way to diagnose a unit. A small block of ice on first row of evaporator will cause a unit that's low on charge to not equalize until the ice melts. Also how cold the evaporator is will determine how quickly pressures equalize, and to what pressure the equalize to. It's easy to mess up and leads guys down wrong path all the time.

    That being said, I don't service residential refrigerators other than a handful of SubZeros at commercial office buildings.

    Sent from my SAMSUNG-SM-G890A using Tapatalk

  16. #13
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    788
    Post Likes
    If you have a critically charged refrigeration system, one with no access fittings and you install access fittings, you just unbalanced the system and will never get the same performance and economy as original. This is why you get the advice to fix electrical and replace if refrigeration side.

    That being said, I remember having a hydraulic tool that would chase a "pig" through the cap tube to remove obstructions. It did work most of the times. That was back when domestic refrigeration was more service friendly.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.