Thread: Nortec Humidifier
-
01-28-2009, 12:59 PM #1
Professional Member
- Join Date
- Sep 2008
- Location
- Central Pa.
- Posts
- 33
Nortec Humidifier
i have a Nortec Humifier Model# NHMC100 giving "Excessive Current Error 1" code. Checked voltages, 460 3 phase unit, wire connections etc. Replaced the cylinder, checked the conductivity of the water and everything. Still getting the alarm and lockout. Any help would be great.
-
01-28-2009, 03:37 PM #2
Professional Member
- Join Date
- Apr 2004
- Location
- Baltimore
- Posts
- 29
Do you know what the current is that it is pulling when calling from humidty? what is the conductivity of the water? I have has some issues and It was a problem with the board. Not sure if any of this helps?
My job is to send a man thats wants big money for little effort to a customer that has a problem but doesnt want to pay for it!
Panic caos and disorder my work here is done!
-
01-28-2009, 04:45 PM #3
Call 613-822-0335 and ask for tech support .
You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
01-28-2009, 06:57 PM #4
New Guest
- Join Date
- Jan 2009
- Posts
- 2
Is the unit draining OK? Or is the the drain stuck with dirt making it drain all the time?
I had that problem this winter but I think it was giving a different alarm.
-
01-28-2009, 08:41 PM #5
Professional Member
- Join Date
- Sep 2007
- Location
- SF Bay Area
- Posts
- 130
Read Grahams' post above.
If this is a regular PM for you, hopefully the operating amps are recorded somewhere on the job site, in your notes, or maybe there is another humidifier on site that you can compare the current amp draw against?
If the humidifier is located outside, moisture can form inside the control cabinet on the control boards and cause nuisance trips. I've only ever seen the current error 1 caused by poor connections or a plugged cylinder drain.
-
01-29-2009, 07:45 AM #6
Professional Member
- Join Date
- Sep 2008
- Location
- Central Pa.
- Posts
- 33
This unit is inside an office building. Conductivity is 70 micromhos ( a little low i think). Each leg is pulling 23-25 amps. On start up the unit will call for 100% demand then the drain solenoid will open for about 3 seconds. It will cycle this way 6 or 7 times, then it seems to be ok. I'll come in the next day and it is off on alarm again. I have a new drain valve, i am waiting for a new fill valve. These items i was told to replace by tech support.
-
03-03-2011, 03:09 PM #7
New Guest
- Join Date
- Mar 2011
- Posts
- 2
NORTEC 100 Humidifier
I am thinking about installing 4 new NORTEC NHTC-100'S in our facility. Does anyone have any opinion about the Pro's and Con's with this humidifier.
-
03-03-2011, 06:00 PM #8
Regular Guest
- Join Date
- Jul 2001
- Location
- Canada
- Posts
- 1,692
J U N K , have 18 on 1 site and nothing but GLITCHES , customer is slowly replacing them
-
03-03-2011, 10:38 PM #9
-
03-04-2011, 11:09 AM #10
New Guest
- Join Date
- Mar 2011
- Posts
- 2
Control Guy
Thanks for the reply. I've been hearing the same thing from other serviceman.
-
03-05-2011, 10:06 PM #11
Regular Guest
- Join Date
- Nov 2010
- Posts
- 16
you need to keep up on the maintenance ,you can go through bottles pretty quick if you have hard water. Install an RO supply if possible it helps.
-
03-11-2011, 04:43 PM #12
Professional Member
- Join Date
- Feb 2006
- Location
- michigan
- Posts
- 175
I have serviced a NHMC200 several times. They are very touchy. You are supposed to clean the drain and fill valve every cylinder replacement. These humidifers are nice when they work but seem to break down more often then not.