    Carrier 19xr

    How come there are no isolation valves on the small filter drier on the side of the compressor
    My customer wants it changed yearly
    Has anyone added valves to these for convenience don't want to affect oil flow


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    May 2012
    Location
    California
    Posts
    535
    Post Likes
    It's a strainer once every 5 years or when machine is open for service. I have never had one plug up.

    Sent from my SM-G900V using Tapatalk

  3. Likes CHILLERSVCMAN liked this post
  4. #3
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    115
    Post Likes
    Why does the customer request a yearly change of the strainer ? Did they have a tube failure and flood the machine ? It is a high pressure machine . As far as isolation valves - a gauge port would need to be added to evacuate , just another potential leak source. Plus another valve someone would forget to open during maintenance . I have added valves when there was a need .