Chattering gas valve
Today I had a service call on a Trane ReliaTel gas pack. M#YSD150F3RHA04000/ S#15021058D When I tested unit in heat it started up went through its step and when the gas valve was energized it started chattering really loud. I had 24 volts going to the valve. So I thought I had a bad valve, but before putting on the new one. I hooked it up to make sure it didn't do the same thing. It worked fine not installed. But as soon as I installed it and tested unit the new valve did the same thing. So confused. Any ideas what may be causing this problem? Make note would not chatter right out of the box.
-
-
Incoming gas pressure?
Sent from my SM-G550T2 using Tapatalk
-
Unfortunately I had a recent van break-in and had all my tools stolen and was not able to check the gas pressure. So I turn the gas off to the unit to check this Theory and it still chattered.
-
Did you relieve pressure in the line after closing the valve?
Nest is POO!!
-
Originally Posted by
HVAC_Marc
Did you relieve pressure in the line after closing the valve?
unfortunately no. I've never run into this issue before. I was so frustrated I had to walk away.
-
that is a negative pressure gas valve. you need the service literature for that type of gas valve, and the proper tools to diagnose.
-
So it sounds like I have a gas pressure problem. So on my return visit this is were I will start. Thank you for all y'all's support on this issue. I hope after correcting the gas pressure this will resolve this issue and if not I will be back..
-
get your post count up and apply for pro status. we share tons of technical data that would be beneficial to you in solving this problem.
-
Thank you. Im new to the site and always trying to fine answers to issues I don't understand. Im a technician always trying to learn and build my skills.. #notafraidtoask about the simple things I should know or the harder ones I don't..
-
Does gas supply come into the bldg at higher pressures than 7" w.c.? If so, the "step down" or secondary regulator on gas supply could be failing. Should be easy to id with suitable range pressure gauge. I have had gas valves completely shut down (as some are designed to do) from high inlet pressure..
I like the concentric tube type. I fill with coffee rather than water (no sugar or cream, please) as it is always at my side and the warm brown gives a beautiful contrast for reading the pressure with an old pair of eyes...
-
Post Likes - 2 Likes, 0 Dislikes
-
7" is nominal, not uncommon at all to see 8.5 or so i believe trane says no higber then 10"
Sent from my SM-G550T2 using Tapatalk
-
Originally Posted by
11austinlee
Today I had a service call on a Trane ReliaTel gas pack. M#YSD150F3RHA04000/ S#15021058D When I tested unit in heat it started up went through its step and when the gas valve was energized it started chattering really loud. I had 24 volts going to the valve. So I thought I had a bad valve, but before putting on the new one. I hooked it up to make sure it didn't do the same thing. It worked fine not installed. But as soon as I installed it and tested unit the new valve did the same thing. So confused. Any ideas what may be causing this problem? Make note would not chatter right out of the box.
Do you have a drip leg in the gas line?
We had a unit that suffered from such a problem without one.
Sincerely,
William McCormick
-
Post offices are notorious for having open interior doors, and running a lot of gas all day long. You can get a lot of liquid in a very cold line moving a lot of gas all day long. A diminishing diameter gas main is important as well.
Sincerely,
William McCormick
-
Originally Posted by
11austinlee
Today I had a service call on a Trane ReliaTel gas pack. M#YSD150F3RHA04000/ S#15021058D When I tested unit in heat it started up went through its step and when the gas valve was energized it started chattering really loud. I had 24 volts going to the valve. So I thought I had a bad valve, but before putting on the new one. I hooked it up to make sure it didn't do the same thing. It worked fine not installed. But as soon as I installed it and tested unit the new valve did the same thing. So confused. Any ideas what may be causing this problem? Make note would not chatter right out of the box.
If you go over what you wrote you might also uncover the variable that you found and mentioned, that will lead you to another possible problem, after the valve.
Sincerely,
William McCormick
-
We went out on a call to a very large commercial industrial building that was turned into smaller commercial spaces, most unoccupied. It had a huge gas main, ten inches in and then eight inches in diameter and perhaps 150' long. But now with much smaller heating units and hot water heaters. Some requiring only a 1/2" feed.
We found that some of the units were failing on a regular basis. The pilots were going out during the night, and the place was ready to start freezing pipes at night. Some of this information came from people that either lived there or worked there.
So we changed a unit that was totally gone, the gas valve was damaged, which made me suspect air in the main. My experience is 99.9 percent of the time it is not the gas valve.
From what people had said about the large flames upon ignition that took a long time to ignite, and would sometimes create flames outside of the unit. I figured it was air in the main. Or someone hooked up a propane tank outside and did not say anything, haha. That really happens. They had people working on it almost everyday. Plumbers, HVAC guys, landscapers, friends, family anyone they could get.
The amount of gas you have to purge is unnerving to say the least. Having purged such mains successfully at a post office I knew exactly how long it takes. And how unnerving it is. You have to keep it flowing or you create a large volume of faulty non-spec gas. Scary has heck though.
An attempt to light the unit prematurely singed my coworkers hair and created quite a pop, as it took out the new gas valve haha. I was instructed not to say a word or else haha. The valve was banging quite a bit, as it would light and go out with a pop, and then finally a boom haha. That does not sound like your problem, however it is something to think about.
The bottom line the building needed to be properly repiped for the new application. Every unit needed a new service valve.
Leaks needed to be fixed before the branch service valves so each technician came in and vented and allowed air into the main pipe.
Sincerely,
William McCormick
-
Usually a chattering gas valve, relay, contactor, or any similar component is caused by a voltage drop. This can be caused by a ton of different scenarios with the low voltage and sometimes with the high voltage side, so do not focus solely on gas supply issues.
-
Post Likes - 4 Likes, 0 Dislikes
-
Originally Posted by
slctech
Usually a chattering gas valve, relay, contactor, or any similar component is caused by a voltage drop. This can be caused by a ton of different scenarios with the low voltage and sometimes with the high voltage side, so do not focus solely on gas supply issues.
X 2
With the valve not installed it's working aginst no pressure so no load on it.
-
Post Likes - 1 Likes, 0 Dislikes
-
He did say it worked while not hooked up to the gas. Its important measure the voltage under a load. Amps of the valve could not hurt either
Sent from my SM-G550T2 using Tapatalk
-
Post Likes - 1 Likes, 0 Dislikes
-
14" w.c. incoming is the maximum the valve is designed for. with that said, please keep in mind that when a valve shuts off, the incoming gas pressure can rise several inches of w.c. also, some gas regulators are not "positive shut off"...they allow a little gas past the valve...this is ok if you have a pilot light but not if you have a hot surface or direct spark ignitor. proper tools are most important. gathering more information than necessary is also a good idea.
"Right" is not the same as "Wise".
Don't step on my favorite part of the Constitution just to point out your favorite part.
Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.
-
Post Likes - 1 Likes, 0 Dislikes
-
Check pre and post regulator for gas pressure. Same scenario a couple years ago, regulator failed.
Sent from my SM-G935T using Tapatalk