    FX40 help...

    I have a facility that has multiple VMA's in a public area, the customer wants the stats locked down. I know how to do this with HVACPro, is there a way to do this through the FX? Or do I have to change in HvacPro, save, and change prn? (nightmare) Can I delete read point add rwpoint for acthtgsp and actclg sp without ill effects?
    He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.

  2. #2
    Join Date
    Nov 2006
    Location
    New Hampshire
    Posts
    255
    Just bring in the warm/cool adjust or remote setpoint ai as a numeric writable and you can override to your heart's content

  3. #3
    Join Date
    Aug 2006
    Location
    Tennessee
    Posts
    433
    Brought WCADJ in and it is showing fault. It is not giving me a fault cause. Do you know the name of the remote setpoint point?
    He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.

  4. #4
    Join Date
    Aug 2006
    Location
    Tennessee
    Posts
    433
    I took COMMONSP to 0.0 and added values for CSP and HSP. I dont think I have seen a point for remote sp.


    WC-ADJ and remote are the same point.
    Last edited by smokeout; 01-21-2009 at 01:05 PM.
    He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.

  5. #5
    Join Date
    Mar 2007
    Posts
    166
    What type of stat is it (digital or slide adjust type)? And are the VMAs N2 or lon?

  6. #6
    Join Date
    Aug 2006
    Location
    Tennessee
    Posts
    433
    1-slide

    2-N2
    He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.

  7. #7
    Join Date
    Mar 2007
    Posts
    166
    We don't currently have any FX40 sites where the customer desired to override the setpoint adjust so the points are mapped in as non-writeable. In NCMs and NAEs though we have customers that do this and it works fine.

    So i would think that mapping AI2 as a numeric writeable should allow you to override it from the FX40.

  8. #8
    Join Date
    Aug 2006
    Location
    Tennessee
    Posts
    433
    WC-ADJ was reading fault because it was at -5 and I guess at lowest setting.
    Overrode point to 0.0 and took CommonSp to 0.0 deg and set CSP and HSP and then it allowed ActSP to be presented. I think I got it. If anyone has a better way, gimme a shout. Thanks.
    He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.