01-21-2009, 12:00 PM #1
FX40 help...
I have a facility that has multiple VMA's in a public area, the customer wants the stats locked down. I know how to do this with HVACPro, is there a way to do this through the FX? Or do I have to change in HvacPro, save, and change prn? (nightmare) Can I delete read point add rwpoint for acthtgsp and actclg sp without ill effects?
He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.
-
01-21-2009, 12:10 PM #2
Professional Member
- Join Date
- Nov 2006
- Location
- New Hampshire
- Posts
- 255
Just bring in the warm/cool adjust or remote setpoint ai as a numeric writable and you can override to your heart's content
-
01-21-2009, 12:17 PM #3
Brought WCADJ in and it is showing fault. It is not giving me a fault cause. Do you know the name of the remote setpoint point?
He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.
-
01-21-2009, 12:23 PM #4
I took COMMONSP to 0.0 and added values for CSP and HSP. I dont think I have seen a point for remote sp.

WC-ADJ and remote are the same point.Last edited by smokeout; 01-21-2009 at 01:05 PM.
He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.
-
01-21-2009, 12:33 PM #5
Professional Member
- Join Date
- Mar 2007
- Posts
- 166
What type of stat is it (digital or slide adjust type)? And are the VMAs N2 or lon?
-
01-21-2009, 12:36 PM #6
1-slide
2-N2He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.
-
01-21-2009, 12:54 PM #7
Professional Member
- Join Date
- Mar 2007
- Posts
- 166
We don't currently have any FX40 sites where the customer desired to override the setpoint adjust so the points are mapped in as non-writeable. In NCMs and NAEs though we have customers that do this and it works fine.
So i would think that mapping AI2 as a numeric writeable should allow you to override it from the FX40.
-
01-21-2009, 03:52 PM #8
WC-ADJ was reading fault because it was at -5 and I guess at lowest setting.
Overrode point to 0.0 and took CommonSp to 0.0 deg and set CSP and HSP and then it allowed ActSP to be presented. I think I got it. If anyone has a better way, gimme a shout. Thanks.He who asks a question is a fool for five minutes. He who does not ask any questions is a fool forever.