    another quality install.....?

    Went on a service call today and found this set-up. It's facing the wrong way! Notice the parts still left on the top. Anyway, the A$$ clowns that put it in are no longer in buisness.
    Attached Images Attached Images   

  2. #2
    Join Date
    Jan 2009
    Location
    plains
    Posts
    35
    Another homeowner gets ripped off. Makes us all look bad.

  3. #3
    Join Date
    Jun 2005
    Location
    North Richloand Hills, Tx.
    Posts
    37
    Any wonder they are out of buisness ......What was service call for..........................

  4. #4
    Join Date
    Dec 2007
    Location
    Afton, VA / Khorat, Thailand
    Posts
    2,468
    I see that kind of crap way too often. Guess some folks just can't flip a coil................
    Tough times don't last...Tough people do.

    Midnight Sun Astrophotography

  5. #5
    Join Date
    Jan 2004
    Location
    Here and there
    Posts
    4,803
    Comfort Specialist I see
    i belong to peta ... people eating tasty animals. all my opinions are just mine.

  6. #6
    Join Date
    Jan 2009
    Posts
    24
    Like the mousetrap

  7. #7
    Join Date
    Jun 2008
    Location
    va
    Posts
    800
    Quote Originally Posted by tincup51 View Post
    Any wonder they are out of buisness ......What was service call for..........................
    Funny you ask.....2 reasons. The customer complained that at night (lately the overnight temps were in the single digits) the indoor temp would fall down to 62 when the stat was set at 70, then run forever before warming up in the day. They also complaned about the outside unit's fan stopping and steam roaring out of the unit....something's wrong with it. When it would do that, they would put it in emergency heat for a while, then switch it back.......

    Well, the second problem, I explained was a "defrost cycle" and is normal., the first was the thermostat's W2 not being hooked up, (W2 to E jumper) so the aux ht wouldn't come on when needed. It only worked when switched to emer ht, thus the installers "F"up, which was expected based on the way it's installed.

  8. #8
    Join Date
    Sep 2004
    Location
    Jersey
    Posts
    389
    Did you address the ductwork, looks like poop. How was the supply trunk coming off the unit.
    I would of gotten fired for that install,
    Very sad to see that work, It just make the good people work harder to get a job and be trusted with contractor like that ot there.
    Ride hard on a Harley!!

  9. #9
    Join Date
    Jun 2008
    Location
    va
    Posts
    800
    Quote Originally Posted by merlin73 View Post
    Did you address the ductwork, looks like poop. How was the supply trunk coming off the unit.
    I would of gotten fired for that install,
    Very sad to see that work, It just make the good people work harder to get a job and be trusted with contractor like that ot there.
    At that point, I didn't want to add insult to their injury. The ductwork was installed around 25 years ago, the equipment there was a changeout done a few years ago. Sadly, what they payed for the changeout was what most people would do the comeplete system with ductwork for.

    That's one of the main reasons the co. is out of buisness, charging very high prices for sub-standard work. Rumor has it they are being sued by a lot of customers for that kind of work and not going back to fix their problems. I recall one job by them that I went on....They charged a lady $750 to braze a small hole in a unit and add a little freon to it. They then turned it on and discovered that the compressor was "locked up" and told her that she needed a new compressor, meanwhile they charged her the $750 anyway just for comming out! They were there for 45 minutes. Needless to say, I got the job to change out the system.