Results 1 to 13 of 38
    Michigan
    Heil high efficiency furnace intake pipe freeze-up
    We had a high efficiency Heil furnace installed a year ago. The last two days have been bitterly cold (below 0) and the furnace was not running correctly, shutting off before getting to temperature, etc. Checked the filters and then told to check the intake pipe outside. Found it to be partially closed off by ice. Again, this morning, same thing happened - cleared out the pipe and furnace again running fine. Any suggestions to avoid this problem altogether?
    Illinois
    Solution is easy...pray for warmer weather
    Other than that...it's happening all over the midwest.
    Quote Originally Posted by thesub View Post
    Do you have two seperate pipes that go out side or do they join together in a pipe in side of a pipe vent kit????
    Michigan
    Yes, there is one for the exhaust and one for the intake - intake pipe has T on the end of it.
    Personally i would install a CONCENTRIC VENT TERMINATION KIT.. It help's keep the intake warm so it might help with your freezing problem. Check out this website.
    http://www.htproducts.com/literature/lp-166.pdf
    Justin
    Jul 2001
    Gold Coast of Connecticut
    Make sure the pipe for the discharge is at least 1 foot above the intake. Look into the installers guide for how they are to be piped.
    Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
    Michigan
    Thanks Freezeking, we had the furnace professionally installed, but both pipes are side by side. Perhaps, we could put an elbow or something on the exhaust pipe and vent it the opposite way from the intake. Would this cause a problem in venting?
    dont think it should cause a problem where in mi u from?
    Apr 2002
    Quote Originally Posted by luv2cruiserccl View Post
    Justin
    A concentric vent kit would work well against horfrost under the OP's tempertures, but I would get the kit that his furnace manufacturer approves
    http://www.ductstrap.com/
    Michigan
    Smile
    Thanks again. Will have my husband look this all over when he gets back tonight. We are located in Midland, MI
    ok not to far have service guys just south of mt. pleasent if you need help
    Northeast Ohio
    Frosted intakes are counting for 75% of our calls right now. The problem will pass, it always does. Concentrics work sometimes but not always. We have found several ways around the problem, call your installer.
    DEM
    Jul 2001
    Outlet must be a Minimum 8" away from the wall and inlet and outlet must be at least 18" apart. I promise you your unit is not properly installed. Also must be at least 12" above the highest anticipated.snow level. Luxaire wants the exhaust 12" above and I have NEVER had a freeze up in 3 years and thats the only brand I install. I think they have something.
    Minimum 18" apart figure 19 page 26.
    http://icpindexing.mqgroup.com/docum...4001105005.pdf