Results 14 to 26 of 29
    Many thanks Carnak.
    I'll give that a try.
    Carnak, after a 2 days of trying, I'm sorry to say I'm struggling to follow your instructions.
    Are you able to dumb it down to the point where I can identify specific columns in the ASHRAE table, and perform a formula to generate the ACCA Grains data? Using Birmingham AL as a control, I need to be able to generate somewhere close to: 34Grains@55%RH / 41Grains@50%RH / 47Grains@45%RH.
    Something like: Cooling Dry Bulb @ 1% minus Mean Coincident Wet-Bulb = etc
    Does the ASHREA table contain enough data to generate these numbers?
    Apr 2002
    Indoor temp 75F
    at 55% RH holds 71.5 grains
    at 50% RH holds 64.9 grains
    at 45% holds 58.3 grains
    Dry bulb 92 and coincidental wet bulb 75 air holds 103.9 grains
    So probably ACCA would say to maintain 55% use (103.9-71.5) = 32.4 grains of mositure in every cubic foot of outdoor air that infiltrates in, used for ventilation in the manual j calc.
    to maintain 50% RH (103.9-64.9) = 39 grains in every cubic foot of infiltration
    to maintain 45% (103.9-58.3) = 45.6 grains
    you can try it for the 0.4% levels, you can also try it keeping it 74F inside.
    Noiw what I get anal about, worst case humidity design
    its 75 degrees outside and the air contains 135 grains of mositure
    now to be able to maintain 55% RH inside, for every cubic foot of air that infiltrates in, you have to remove at least 135-64.9 grains = 70.1 grains.
    how often does the AC run when it is 75 and cloudy? Need a tight structure to keep infiltration out and some internal gains to get the ac cycle on/off
    http://www.ductstrap.com/
    Apr 2002
    Apr 2002
    if you know two things about the air, the pysch chart will give you all the other air properties, like Grains of moisture, the dew point, specific volume, the enthalpy etc
    Carnak
    Do I understand that these RH figures are constant at an indoor 75f? i.e.
    55% RH = 71.5 grains
    50% RH = 64.9 grains
    45% RH = 58.3 grains
    If so, I need only be concerned with the outside conditions which vary to calculate the grains differance?
    How did you resolve 103.9 outside grains by inputting "Dry bulb 92 and coincidental wet bulb 75 air". Is there a table or formula that you use?
    Apr 2002
    its called the psychrometric chart
    you need to search for it here, online
    I gave a link to some free demo programs, see post 17 & 18
    75 is a common indoor design temperature, maybe ACCA uses 74, maybe they take the outdoor condition a little different on the dry bulb wet bulb
    For an indooor temperature of 75F and RH of 55,50 & 45 percents, you use the chart to find 71.5, 64.9 and 58.3 grains of mositure
    then you use the chart to find the grains of moisture in the outdoor air.
    ACCA grains are the difference between the mositure indoor and outdoor.
    Apr 2002
    trane sells a laminated 11x17 chart, has good examples on the back
    Carnak
    This is nice little utility but it doesn't state the grains figure.
    http://www.sugartech.co.za/psychro/index.php
    Have found a better online calc that does the job.
    http://www.envirochex.com/Psychro.htm
    Thank you very much for your ongoing advice Carnak, I'm pleased I got there in the end!
    Much appreciated.
    Apr 2002
    Quote Originally Posted by unclebingo View Post
    Carnak
    use IP units, multiply humidity ratio by 7000 to get grains
    Apr 2002
    Much appreciated.
    you're welcome, don't fall victim to GIGO read up on the topic
    Garbage In Garbage Out, right.
    I've noticed there are disparities between ACCA and ASHRAE data when calculating design grains difference between inside / outside grains.
    Birmingham AL - ACCA
    45% - 47
    50% - 41
    55% - 34
    Birmingham AL - ASHRAE
    45% - 45.53
    50% - 38.93
    55% - 32.33
    Indoor assumes 75F dry bulb on both. ACCA seems to round up 2 grains?
    If only the outside Dry Bulb and Coincident Wet Bulb figure could easily be calculated without the need of an online tool. Otherwise I could enter the formula in the Excel sheet and let it generate the numbers.