Thread: Subcooling

  1. #1
    Join Date
    Jul 2006
    Posts
    133
    Post Likes

    Subcooling

    Hey guys. 3rd year commercial/residential mechanic here. I'm getting conflicting info from different sources regarding subcooling, so I thought I'd ask here to see what you guys thought. TXV system...As my head pressure falls (getting colder outside) my condenser is going to run cooler.

    As the temperature/pressure falls in the condenser...more liquid will start to back up in it. As more liquid backs up, subcooling increases... True or false.

    Cheers.

  2. Likes hedrash liked this post.
  3. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    If ambient temp is the only thing that changes...false. You will get less subcooling as the ambient drops.

  4. #3
    Join Date
    Jul 2006
    Posts
    133
    Post Likes
    Thread Starter
    Quote Originally Posted by jayguy View Post
    If ambient temp is the only thing that changes...false. You will get less subcooling as the ambient drops.
    Hey Jayguy. Thanks for the reply...

    Ok. I don't understand how that's possible. I do understand that when charging, as I add more refrigerant to the system my head pressure increases as well as my subcooling. Fine. Add gas to increase subcooling.

    However, sometime later, if the outside ambient temperature drops, it allows the condenser to run cooler. A cooler condenser means more liquid. More liquid means more time for it to subcool(no?). I would think that as the outdoor ambient drops, subcooling increases. Cooler condenser, more liquid, more time to subcool...

  5. #4
    Join Date
    Dec 2015
    Location
    TN
    Posts
    355
    Post Likes
    On a TXV system you should charge it based on superheat. With a piston you wanna pay more attention to SC.


    Sent from my iPhone using Tapatalk

  6. Dislikes AEW disliked this post.
  7. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Don't think about "cooling." That's where intuition is misleading you.

    This value is based on DIFFERENCE of temperatures.

    When it is hotter outside, and head pressure rises (with the higher condensing temperature) there is a greater difference between the temperature of the liquid line and condensing temperature.

    More difference = more subcooling.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #6
    Join Date
    Dec 2015
    Location
    TN
    Posts
    355
    Post Likes
    Nice way to put it time.


    Sent from my iPhone using Tapatalk

  9. #7
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,117
    Post Likes
    Quote Originally Posted by PaulServiceTech View Post
    On a TXV system you should charge it based on superheat. With a piston you wanna pay more attention to SC.


    Sent from my iPhone using Tapatalk
    NO ! ! ! ! ! Not on residential space cooling. TXV~subcooling, fixed ~ superheat.

  10. Likes kdean1 liked this post.
  11. #8
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,251
    Post Likes
    Quote Originally Posted by PaulServiceTech View Post
    On a TXV system you should charge it based on superheat. With a piston you wanna pay more attention to SC.
    Oops! A little dyslexia here?
    Instead of learning the tricks of the trade, learn the trade.

  12. #9
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Quote Originally Posted by PaulServiceTech View Post
    On a TXV system you should charge it based on superheat. With a piston you wanna pay more attention to SC.


    Sent from my iPhone using Tapatalk
    You have these mixed up Paul, reverse it and you are good.
    But in reality, both should always be taken into consideration, when "troubleshooting", regardless of txv/piston.

    Loss of subcooling with pressure drop... similar to loss of subcool on long vertical rise due to pressure drop, then run it (liquid line) uninsulated through hot attic and watch it flash (zero subcool) at the valve!
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  13. Likes hedrash liked this post.
  14. #10
    Join Date
    Jul 2006
    Posts
    133
    Post Likes
    Thread Starter
    Quote Originally Posted by PaulServiceTech View Post
    On a TXV system you should charge it based on superheat. With a piston you wanna pay more attention to SC.


    Sent from my iPhone using Tapatalk
    Hey Paul. I think you have it backwards, as that's exactly the opposite of what I was taught in school. Fixed orifice is charged by superheat. TX is charged by subcooling, however this isn't about charging, it's about what happens to subcooling with changing outdoor ambients.

  15. Likes hedrash liked this post.
  16. #11
    Join Date
    Dec 2015
    Location
    TN
    Posts
    355
    Post Likes
    Quote Originally Posted by BNME8EZ View Post
    NO ! ! ! ! ! Not on residential space cooling. TXV~subcooling, fixed ~ superheat.
    Oops. I'll stick to refrigeration


    Sent from my iPhone using Tapatalk

  17. Likes kamersoutdoor, hedrash liked this post.
  18. #12
    Join Date
    Dec 2015
    Location
    TN
    Posts
    355
    Post Likes
    Quote Originally Posted by desol View Post
    Hey Paul. I think you have it backwards, as that's exactly the opposite of what I was taught in school. Fixed orifice is charged by superheat. TX is charged by subcooling, however this isn't about charging, it's about what happens to subcooling with changing outdoor ambients.
    It's been a long day lol


    Sent from my iPhone using Tapatalk

  19. #13
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,251
    Post Likes
    Quote Originally Posted by PaulServiceTech View Post
    It's been a long day lol
    I know that feeling well.
    Instead of learning the tricks of the trade, learn the trade.

  20. Likes hedrash liked this post.
  21. #14
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by timebuilder View Post
    Don't think about "cooling." That's where intuition is misleading you.

    This value is based on DIFFERENCE of temperatures.

    When it is hotter outside, and head pressure rises (with the higher condensing temperature) there is a greater difference between the temperature of the liquid line and condensing temperature.

    More difference = more subcooling.
    Neither of the above. On some systems SC will rise, on others it will drop. On others it will first drop and then rise as ambient drops further. See the attached SC chart (cooling mode) in the center of the attached image. Subcooling depends upon several variables.
    Attached Images Attached Images  

  22. #15
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    I can't see the chart with sufficient definition to read it.

    However, I have found that with all of the other variables being equal, it is still a difference value that tends to rise with condensing temperature, and decrease with a decrease in condensing temperature.

    If other variables also change, than the outcome will change.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  23. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    It is also important to note that subcooling is just a temperature difference number. It is not a linear measure of how much liquid is in the condensing unit. It is a number we use to give us an idea about the amount of liquid that is available to leave the condenser via the liquid line.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  24. Likes hedrash liked this post.
  25. #17
    Join Date
    Jul 2006
    Posts
    133
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    It is also important to note that subcooling is just a temperature difference number. It is not a linear measure of how much liquid is in the condensing unit. It is a number we use to give us an idea about the amount of liquid that is available to leave the condenser via the liquid line.
    Hey Timebuilder. I'm following you but I'm not.

    Can you expand a little more on the second half of your statement. Cheers.

  26. Likes hedrash liked this post.
  27. #18
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    Neither of the above. On some systems SC will rise, on others it will drop. On others it will first drop and then rise as ambient drops further. See the attached SC chart (cooling mode) in the center of the attached image. Subcooling depends upon several variables.
    while you are correct that subcooling depends upon several variables, the chart shows "subcooling required" not necessarily what the sub cooling will be at various temperatures...i can not say if the subcooling at 1 point on this chart will be the subcooling at a different point on the chart without the addition of more or less refrigerant...i don't know this company or equipment or what the chart is used for.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  28. #19
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by jayguy View Post
    while you are correct that subcooling depends upon several variables, the chart shows "subcooling required" not necessarily what the sub cooling will be at various temperatures...i can not say if the subcooling at 1 point on this chart will be the subcooling at a different point on the chart without the addition of more or less refrigerant...i don't know this company or equipment or what the chart is used for.
    You could say the same about any SH chart. What would be the point in plotting the required SH or SC at different conditions if each entry corresponded to a different total charge?
    Last edited by hvacrmedic; 07-15-2016 at 09:59 PM.

  29. #20
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    You could say the same about any SH chart. What would be the point in plotting the required SH or SC at different conditions if each entry corresponded to a different total charge?
    again, i don't know what this chart is used for...is it a charging chart or is it an engineering chart? does anything else change as the temperature drops on the units this chart is associated with? such as fan cycling or some other head pressure control? does the chart indicate a constant load or constant indoor WB/DB situation or are they assuming there are some changes?

    i don't know.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •