    I would say the circuit is not making to the fan in stage 1. Sounds like a control issue.

  2. #22
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    Quote Originally Posted by timebuilder View Post
    I have worked on many dozens of energence units. Not one has an unloader.
    It should be, the unit number that was given has an ECM blower, I don't know why it wouldn't.

    Example; LGH060H4ES1G, This is a model that I care for about 50 of, across various sites. All the same, 2 stage scrolls, all. There are a handful of 3 tonners, too. Those for some reason come either way, single and two stage compressors.

    Anyway, sounds like OP may need to update the Prodigy firmware. An M2 board of that vintage may or may not be USB-flashable.

  3. #23
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    When I run that model number, I come up with a brochure that shows an M3 controller. I would think that latest version would be able to take whatever updates are needed.

    I have several with the ECM blower, too.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #24
    Join Date
    Apr 2016
    Posts
    67
    Post Likes
    Quote Originally Posted by timebuilder View Post
    I have worked on many dozens of energence units. Not one has an unloader.
    I have not worked on a lot of Lennox equipment. Most of it it I see is old and at least ten seer and runs fine because it was taken care of. But I seem to remember an old condensing unit that had a two speed hermetic in it. And I think they were separate motors too. It was shees 22 years ago. Does that sound right?


    Two wrongs don't make a right but three lefts do.

  5. #25
    Join Date
    Feb 2008
    Location
    Western Wa.
    Posts
    3,542
    Post Likes
    Bad condensor fan cycling switch?

    Follow the schematic
    UA Proud

    "Phfft! Facts. You can use them to prove anything." Homer Simpson

  6. #26
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    It has an M2 board. A 2010 unit predates the M3 by several years.

    Lennox is funny like that. Because the models numbers have been in use for so long, when you search for info with just the model number, you'll get the most current version, not necessarily what you actually want. It's ok, normally, because other than the controller, there's generally no other substantial changes in the series, at least none that make the documentation useless.

    The unit in question is a 2010 unit with a "1" revision code. I already knew from the age it had to be an M2, and DaveNet confirmed it from the serial.

    Anyway, I guess this has nothing to do with OPs actual problem. How is the unit being controlled? Tstat or network? Does the fan come on in test mode?

  7. #27
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Yes, I had already decided that the published info was wrong. Google produced the correlation between the model number and the brochure. No M3 controllers were floating about in 2010.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #28
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Ernest Crossman View Post
    I have not worked on a lot of Lennox equipment. Most of it it I see is old and at least ten seer and runs fine because it was taken care of. But I seem to remember an old condensing unit that had a two speed hermetic in it. And I think they were separate motors too. It was shees 22 years ago. Does that sound right?


    Two wrongs don't make a right but three lefts do.
    To the best of my memory, the older GCS units had a small recip in them, a single speed hermetic.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •