Thread: How to remove air from running chilled water system

  1. #1
    Join Date
    May 2016
    Posts
    1
    Post Likes

    How to remove air from running chilled water system

    we have 1100 tons chilled water system which was recently been drained for tie in of chilled water line for the expansion of accommodation building after that water was filled during water filling & after startup of chillers we were purging air from the systems for about 10 to 15 days & then there were no air coming from the air vents. we thought that system is free from air & since it was winter there where no cooling issues. But Now in summer less cooling in rooms complain started coming 7 we observed there is still air in the system. Accommodation complex consist of 6 blocks of ground +1st floor with approximately 300 rooms & 30 AHUs.please advice the best way to remove air from the system. Accommodation complex consist of 6 blocks of ground +1st floor with approximately 300 rooms & 30 AHUs

  2. #2
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Bleed the remaining air from each of the 30 air handling units individually.

    After doing so, recheck the main system at the top.

    Don't forget to check your water chemistry.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •