JCI PMI question
It's been way too many years since I last played around with PMI, so I've forgotten a couple things - today I needed to map in some points when the end user replaced a failed LCP with a DX-9100. Anyway, I need to take the OAT from a nearby AHU, and map it into an ACO on the DX. Since I never learned GPL, is there another way to do this?
-
01-06-2009, 08:15 PM #2
Banned
- Join Date
- Mar 2006
- Posts
- 3,641
-
01-06-2009, 10:31 PM #3
GPL would be the easiest. You can also use JCBasic
Following example creates an object "Export" that you can download to the NCM after you compile it.
=============
PROCESS 'DX-SYS\Export' "" '\NC-NAME'
PERIOD 00:05:00
PRIORITY 4
TELL 'DX-SYS\OAT' TO "SET_AOS" 'AHU-SYS\OAT\VALUE',2
END PROCESS
===========
Replace following with names applicable to your system
DX-SYS\OAT = System and point name for OAT in system used by DX9100 (the ACO)
AHU-SYS\OAT = System and point name for OAT in system used by AHU
NC-NAME = the name of of the NCM
-
01-07-2009, 12:52 AM #4
Professional Member
- Join Date
- Dec 2004
- Location
- San Francisco Bay Area
- Posts
- 434
Thanks guys - I'd totally forgotten about JCBASIC (I told you it'd been a few years...), and you can't get much more precise an answer than ex's...thanks, exwtk!
-
01-07-2009, 12:16 PM #5
JC Basic
I added some more lines that could let you select the lowest outside air temperature if you have more than one sensor!!!!!
PROCESS 'DX-SYS\Export' "" '\NC-NAME'
PERIOD 00:05:00
PRIORITY 4
IF 'AHU-Sys1\OA-t' >= 'AHU-Sys2\OA-t' then
OAT' = 'AHu-Sys1\OA-T'
else
OAT' = 'AHU-Sys2\OA-T'
TELL 'DX-SYS\OAT' TO "SET_AOS" 'AHU-SYS\OAT\VALUE',2
END PROCESS
===========
Replace following with names applicable to your system
DX-SYS\OAT = System and point name for OAT in system used by DX9100 (the ACO)
AHU-SYS\OAT = System and point name for OAT in system used by AHU 1/2
NC-NAME = the name of of the NCM Process
-
01-07-2009, 02:26 PM #6
Professional Member
- Join Date
- Dec 2004
- Location
- San Francisco Bay Area
- Posts
- 434
And all went well, until PMI reported that the compiler wasn't installed, adn to contact Johnson for the software - yeah, I don't think so... Now the customer's own "controls expert" can finish up that little piece.
Thanks again for the help!
-
01-07-2009, 07:09 PM #7
-
01-10-2009, 12:27 AM #8
Your right here's the corrected JC Basic. Also most outside sensors will read differently!!!!
PROCESS 'DX-SYS\Export' "" '\NC-NAME'
PERIOD 00:05:00
PRIORITY 4
IF 'AHU-Sys1\OA-t' <= 'AHU-Sys2\OA-t' then
OAT' = 'AHu-Sys1\OA-T'
else
OAT' = 'AHU-Sys2\OA-T'
TELL 'DX-SYS\OAT' TO "SET_AOS" 'AHU-SYS\OAT\VALUE',2
END PROCESS