Page 1 of 5 12345 LastLast
Results 1 to 13 of 57
Thread: adjusting txv's
    Dec 2008
    adjusting txv's
    i came across this a few times already in my 2 year career, today on a walk-in fridge top half of evap is iced up, txv iced up at distributor, good airflow, clean evap, fans run, checked pressures after de-icing, 35/205 r-22, full sight glass. didn't suspect charge issues with a full sight glass. high superheat at evap 30 degress. opened up the txv a few turns got the superheat to 12 degrees. everything seemed to run well after that
    my question is, why would the txv need to be adjusted all of a sudden?, this walk-in has always ran well for the two years i've been servicing this restaurant, have never had isssues, is the txv getting restricted and i'm compinsating by opening it up some more? or is it slowly crapping out, or is that normal to need to adjust txv's at times ?
    florida
    Your power head could be week or your pins sticking.
    Educational forums are open.
    Jun 2001
    Michigan
    did you check the liquid inlet screen to the TXV.
    Nov 2005
    was the box temp within 10* when checking that superheat reading?
    Dec 2008
    yes, box temp was 45 degrees when i checked original superheat
    Aug 2008
    There are several possible reasons. But likely the power head has lost a very small amount of its charge, so then the spring pressure to power head pressure was out of whack, and you put in back in line when adjusted. Or a previous tech adjusted it when it wasn't the problem, and this was truly a call back.
    florida
    So swinginutters have you been back? give us a up date.
    Canada
    its mechanical, so its normal to be adjusted each few months, with the new electronic txv we will not have this problem, superheat adjusted= good refrigeration cycle= life time compressor.
    Vancouver , BC
    Quote Originally Posted by balzano View Post
    there is an electronic txv now i havent seen that yet?
    Quote Originally Posted by neumonic View Post
    yes, there is and has been one for a lil while now
    and we would glady use your money to purchase this new electronic valve
    and, lmao
    we have blamed pushrods, inlet screen, and powerhead loss of charge... what about installation? is the thing installed properly?
    is the sensing bulb in the right location? what o'clock position is it on the suction line? is it on a vertical line? is it mounted in an oil trap?
    i don't understand why someone would think a txv needs to be constantly adjusted
    the only thing a TXV does, is adjust and maintain SH. right?
    North Queensland, Australia
    You've got your stepper valves that sense system SH with pressure transducer and temp sensor to compute superheat and drive the valve open or closed incrementally.
    You've got your liquid injection valves that open on increase in superheat to squirt liquid through an orifice. They're an on / off type valve. They can be controlled the same as the stepper or with an inlet an an outlet temp sensor to work out the SH. Have you ever walked into a supermarket refrigerated section and heard a clicking from the cases? That's the injectors opening.
    Then there's the old thermal type valve that has a variable resister in the suction line that feeds current to a heater in the top of the valve where yout TX valve power element sits. If I recall correctly, the heater heats a bimetallic disk that flexes in and out to drive pins as in a normal TX valve. It's the simplest of the 3 as it needs no electronics.
    Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002
    Vancouver , BC
    i have only been in the trade a very short 2 years so i havent seen much yet thats why i was interested....ive seen the eeprs , just not any electronic txv
    How do they operate?