    walk in box help

    I dont do any refrigeration but i was asked a question, i dont have many details but any help would be appreciated. Walk in box with outdoor c/u,R-12,pressure switch operating control cuts in @34#, cuts out@19#, maintains about 42*, cch is good. Problem is when it gets cold outside ( below 20*)box satisfies , pressure never gets above 19# to cut comp. back in. Box temp continues to climb and comp does not come back on until outdoor ambiant goes above 20*, any help would be appreciated and sorry in advance for sketchy details.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Install a t-stat and LLSV.

    Use pressure control for pumpdown only. Set is quite a bit lower. Only to prevent operation in a vacuum.

    She will run.



  3. #3
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Install a t-stat and LLSV.

    Use pressure control for pumpdown only. Set is quite a bit lower. Only to prevent operation in a vacuum.

    She will run.
    Ditto that.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  4. #4
    Join Date
    Jul 2006
    Location
    N.Y., N.J.
    Posts
    131
    Post Likes
    Thread Starter
    Thanks for the quick response, i was thinking along the same exact lines but needed a confirmation. Have a great new year.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    FYI Starting point for R-12 Cut in / Cut out 36 & 16.

    Remember the rules: Refrigerant migrates to the coldest point, Warm Moist Air Migrates to a cool dye enviroment.

    With that said:

    Refrigerant migrates to the coldest point. CCH is keeping it from condensing to a liquid in the crank case but the receiver / discharge line / condenser are still at ambient. ( Including the cylinders )The LP control senses this. As others have said, T-Stat with LLS valve is the only cure & Reset LP control as a safety only.

  6. #6
    Join Date
    Jul 2002
    Location
    NY
    Posts
    1,887
    Post Likes
    How is the head psi controlled?
    Last edited by itsamine; 01-03-2009 at 10:27 PM. Reason: Read entire post.
    Not what it use to be

  7. #7
    Join Date
    Jul 2006
    Location
    N.Y., N.J.
    Posts
    131
    Post Likes
    Thread Starter
    I havent seen the set up yet, so i dont know how the head pressure is controlled , all the info that i have was related to me by the tech. who set it all up. Ill relay what new info i have and hope it works.

  8. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by finest View Post
    Problem is when it gets cold outside ( below 20*)box satisfies , pressure never gets above 19# to cut comp. back in. Box temp continues to climb and comp does not come back on until outdoor ambiant goes above 20*.
    And what’s the standing pressure of R-12 @ 20*F?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •