    Condenser fan

    I have a used Traulsen URS-36-DT and the consenser fan does not seem to be behaving correctly. Essentially, it is always running, regardless of whether either of the compressors is running. I know this is not standard, but is it possible that it is designed that way for this unit? The other odd thing is that it only runs if both the refrigerator and freezer are switched on (at the switches, not the cold control). So I cannot turn the freezer off and have the condenser fan run for the refrigerator for instance. (Actually, I can, by turning off the freezer with the thermostat, but not with the switch). Is this wired incorrectly, or is there a part that is not working correctly?

  2. #2
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    3,411
    Post Likes
    Post a picture of it.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,677
    Post Likes
    How about checking or posting the wiring print?

    Certain DPDT stats function that way. ON closes one contact and the second contact closes at setpoint.

    If the ON contacts are wired in series, then what you are describing is exactly correct.



  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,455
    Post Likes
    This is the domestic model Traulsen, 2 compressors and 1 condenser.

    There is a relay that brings on the fan if either switch is on.

    I have a wiring diagram on PDF if you need it

  5. #5
    Join Date
    Nov 2012
    Posts
    2
    Post Likes
    Could I possibly get the wiring diagram from you. Thank you

    Manuel

  6. #6
    Join Date
    Jul 2011
    Posts
    2
    Post Likes
    Attached. The (rather untidy) blue add-ins are for the relay I added to stop the condensor fan running when both compressors were off. Good luck.
    Quote Originally Posted by mxavierr View Post
    Could I possibly get the wiring diagram from you. Thank you

    Manuel
    Attached Images Attached Images

  7. #7
    Join Date
    Nov 2012
    Posts
    2
    Post Likes
    Thank you.

  8. #8
    Join Date
    Dec 2008
    Posts
    8
    Post Likes
    Thread Starter
    If I understand the wiring diagram, the condenser fan does indeed run all of the time, although it should come on with either switch on, so I would guess there is something wrong with the relay. It is no big deal unless one side gets left on for a while with the other side off.

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,455
    Post Likes
    Any SPDT 110V coil relay will work. That’s a 9 or 16W motor.

  10. #10
    Join Date
    Nov 2008
    Location
    Hudson Valley, NY
    Posts
    219
    Post Likes
    If this is a resadentle it is probly not a lot of air flow through condensor
    I would keep it runing all the time
    two compressor's one condensor and not much air flow

  11. #11
    Join Date
    Jun 2006
    Location
    Omaha, Nebraska
    Posts
    882
    Post Likes
    Running the condenser fan without a compressor is pointless unless you're trying to get your electric bill up. Surely that cannot be what the engineer planned. Is there maybe a pressure switch in series with the fan set too low or stuck? Something is not right.

  12. #12
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    3,411
    Post Likes
    Quote Originally Posted by man from trane View Post
    Running the condenser fan without a compressor is pointless unless you're trying to get your electric bill up. Surely that cannot be what the engineer planned. Is there maybe a pressure switch in series with the fan set too low or stuck? Something is not right.
    Tell that to Silver King. Their condensor fans are wired to run 24/7. I think it might be planned obsolescence. You know the quicker the condensor gets packed with dirt. The more likely the cap tube gets plugged that leads to compressor failure. Or their just looking out for us service techs. Keeping us employed.

  13. #13
    Join Date
    Dec 2008
    Posts
    8
    Post Likes
    Thread Starter
    There is nothing in the circuit but the master switches and the relay. It is a single condenser (and fan) with two compressors. It is designed to be built in, so the ventilation needs to be good. That said, it is a fifteen-year-old unit, and may simply be an older design less focused on efficiency.

    It seems that it would be fairly straightforward to wire it so that the fan would only got on when one of the compressors did, but I don't want to do this if it is a bad idea. Does anyone know if the current UR48 models use the same design?