    Help: Weil McClain Ultra 105 Lockout Issue

    I recently (November 17th) purchased a WM Ultra 105 with the help of this forum and had it installed by a local Union plumber in NJ. He installed 3 zone baseboard system in addition to indirect WM H/W heater. The system works great with one exception. The boiler, when being called for Baseboard heat, after about 10-15 minutes, goes into soft lockout with error code: Return > Supply. I have read on several forums there is sometimes an issue with Supply water too fast, but have not found anything on Return > Supply.

    The local plumber could not find anything wrong with the system nor could another contractor. We have been trying to get a hold of someone at WM with no luck.

    I have recorded the last two lockout stats:
    Supply: 178 166
    Return: 161 153
    Target: 180 180
    outdoor: 33 32

    I have tried moving the sensors in different positions hoping that would possibly solve the issue. My plumber is curious if there is anything else he can do to troubleshoot the issue? We still have phone calls into WM hoping to have them returned!

    Any help would be great as it is soft lockout for the first 20 resets. After that, it goes to hard lockout until you reset it.

    The Boiler Manual shows an error for Supply > Return but nothing for Return > Supply

    If anyone has any ideas, please help!

  2. #2
    Join Date
    Jul 2006
    Location
    NJ
    Posts
    239
    Call a professional to check it out. Goto Weil-Mclain's web site to find a contractor to see whats the problem.

  3. #3
    Join Date
    Nov 2004
    Posts
    1,009
    please read the site rules. NO DIY advise is given.

  4. #4
    Join Date
    Oct 2008
    Posts
    6
    Completely understand no DIY and understand it's all professionals livelihood! I was simply asking for other professional advise as my plumber and another contractor could not fix the issue and had no where else to turn.

    Update: I was able to get a hold of a tech at WM and the issue is now resolved. While my contractor reversed the thermostats, he never cycled the unit causing them to continue with their old readings and not reset. Once reversed AND reset the issue was corrected.

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,520
    Actually, it does have a section for return > supply.

    Its usually an installer error, or forgotten step.

    Let him read the manual, it has suggestions.
    Contractor locator map

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Feb 2006
    Posts
    96
    is it a series 2 or 3?
    can you take a picture of the piping?

  7. #7
    Join Date
    Jul 2006
    Location
    NJ
    Posts
    239
    I would be intrested in a pic too. Ive came accross many Ultra systems that were not pipe correctly and people were getting the lock-out problem.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •