    boiler pressure dropping

    got a new boiler and the pressure gauge drops erratically from time to time locking the boiler out until the manual feed valve is opened for a second and pressure is restored. Air eliminator is open and very sure of no leaks. Could this be a trapped air pocket in the system that once in a while works its way near the gauge or limit switch to drop pressure?? could use some advice

  2. #2
    Join Date
    Dec 2006
    Location
    New Jersey
    Posts
    747
    hot water or steam?

  3. #3
    water...thanks

  4. #4
    Join Date
    Dec 2006
    Location
    New Jersey
    Posts
    747
    what kind of boiler? usually the pressure rises when its heated.

  5. #5
    Join Date
    Feb 2003
    Location
    pittsburgh,pa
    Posts
    727
    Sounds like you need to call a service tech. manually feeding water to a closed loop water system is not right. By introducing untreated water continuously will cause sediment build up leading to heat exchanger failure.Boiler should be equipped with a lwco and a auto feed valve. So in the event of low water it should temporary rectify issue. You my be heading for bigger issues later on

  6. #6
    its a munchkin 80m, the pressure will be good for days or weeks then out of the blue the pressure is a zero and its locked out. i'll open the manual water valve for a split second then the pressure jumps to 12psi and fires. happened maybe five times this winter

  7. #7
    Join Date
    Jan 2008
    Location
    Outside The Motor City
    Posts
    666
    are you pumping away???

  8. #8
    Join Date
    Aug 2006
    Location
    Wisconsin
    Posts
    1,504
    Call the installers back if it is new. May have a bad exp tank.
    Buy American! The job you save may be your own.

  9. #9
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,804
    Call the installer, somethings not right. I have several ideas but since this is not a DIY site, I can't help
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  10. #10
    Join Date
    Dec 2006
    Location
    New Jersey
    Posts
    747
    was your fill valve and backflow changed when they installed it? how hard is your water? this changes everything at first u said as it ran the pressure would drop every heating cycle. Is your fill valve set properly?

  11. #11
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,826
    You should never have to manually operate the auto-fill valve. Minute leaks will invariably allow the boiler pressure to drop over serveral weeks. The auto-fill is not responding. Call your installers back and have them change it out or properly adjust it while it's in warranty.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  12. #12
    Join Date
    Dec 2006
    Location
    New Jersey
    Posts
    747
    80 m is that the little black boiler. if so i just installed on the other day. replaced a hydropulse.

  13. #13
    Join Date
    Oct 2002
    Location
    Yo.... Here!, I'm right here..
    Posts
    6,236
    Popcorn.......getch ya popcorn hea......Popcorn getch.a popcorn.......hea.......

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event