    Offsetting Point value in FX60

    Thanks in advance for any help on this problem. I have a humidity value that is consistently 15% higher than the actual space humidity. Is there anyway to enter an offset for that point in the FX60 Wiresheet and have the fxo7 recognize the offset value and control to the new value?

    Thanks again

  2. #2
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    730
    Post Likes
    If the person that programmed the FX07 set up the AI point(s) offset slot, then yes. Otherwise no.

    Best practice is to calibrate or replace the humidity transmitter.