  1. #14
    Join Date
    Jun 2006
    Posts
    281
    Quote Originally Posted by freddy-b View Post
    Yes.
    Thanks again
    K

  2. #15
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    511
    That's how I see it. Actually I did this with 2 networks.

  3. #16
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    511
    Quote Originally Posted by freddy-b View Post
    There can be up to 5 jcin2networks. so multiple N2 addresses from the
    existing five N30's would not be the issue.

    If I understood you correctly?
    I understand the software can apply 5 networks, but how can it choose which multiple addresses to contact on the hardware side. There must some reasoning for the 5 N-30s in the same panel, line length perhaps.

  4. #17
    Join Date
    Mar 2008
    Location
    NW Ohio
    Posts
    949
    freddy-b, for general consumption, please address mechdorn's question.

  5. #18
    Quote Originally Posted by NINAX View Post
    freddy-b, for general consumption, please address mechdorn's question.
    I dont think I can.

  6. #19
    Join Date
    Jan 2007
    Posts
    167
    Each of the 5 N2 buses would be on isolated COM ports on the Jace. So you could have an N2 device with address 10 on each bus, and the Jace designates them differently because they are on COM1, COM2, etc.

    You still have the same limitations that on any given segment that you cannot duplicate an address.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event