Results 1 to 13 of 19
    Jun 2006
    How many N2 buses on a fx60?
    I know 2 has been done before but how about 5?
    We have a site with 5 partially filled N30's and we would like not to have to recable the place, or keep the N30's and do BacNet.
    Thanks in advance
    kevin
    Feb 2007
    It all depends on the number/type of devices on each segment
    Jun 2006
    I was wondering if there is a driver limit about dealing with 5 busses at once or a liscenceing problem
    thanks
    kevin
    NW Ohio
    Quote Originally Posted by kevin stone View Post
    thanks
    kevin
    No there is not, unless they've changed it very recently.
    I've never seen a limit.
    Jun 2006
    Kevin
    I would consider this replace the 5 N-30's with 5 FX-20's add an FX server and your good to go. Why load up an FX-60 ? If it crashes you loose access to your whole site. The N2 trunks can stay put no electrical labor to cover. Room for expansion down the road and a happy customer. Just my opinion thats all.
    GB
    Mar 2006
    It will take 5 with no license problems. We have one with three, 2 loaded heavily and the third relatively light...and the EM60 still has alot balls left.
    But I agree with Cal1, if the 5 n2 trunks are not reasonably spaced together, that could be more trouble than its worth.
    As far as The N30/Bacnet thoughts...dont do it man...dont do it!
    Jun 2006
    Thanks Guys
    The 5 N30's are in the same cabniet so cabling is not a problem.
    There is virtually no budget for this job (typical for this coustomer)
    so I will try the 5 busses
    thanks again.
    Kevin
    Ps:So Freddy not ready to take a crack at my Modbus post ?
    Mar 2006
    Thanks Guys
    thanks again.
    Kevin
    Because I have never seen your issue, and in any case you have already done the things I would of suggested.
    So I was waiting for one of the wizbangs answers.
    Near Philly
    I guess the problem is multiple addresses. If you can combine a couple of the networks into one, buy the expansion module for the additional (2) RS-485 networks, it would work just fine.
    Mar 2006
    Quote Originally Posted by mechdorn View Post
    There can be up to 5 jcin2networks. so multiple N2 addresses from the
    existing five N30's would not be the issue.
    If I understood you correctly?
    Jun 2006
    I am making the assumption that bus #1 can have a controller #1
    and bus #2 can have a controller #1 and so on is that correct?
    Mar 2006
    Yes.