Results 1 to 13 of 13
    Jun 2006
    West Texas
    Thumbs up ABCS Guys I need your help!!
    I recently install several JCI TEC-2104-3 multistage 2H2C with economizer controllers. They work great and they are really an expensive device. My problem is, does anyone know what the ADI or AO info is for the outside air damper? It would really be nice to see what the economiser is dooing without having to go to the unit with a DVM. The prn file JCI points you to is a generic "fits all" so that's no help. TIA for any information.............rrh
    Somewhere, WI
    I have a couple prn's for tec's but none for 2104, I can email to you if you want. It looks like they don't use AO points, only ADI's. Try adding ADI points until you have a value match.
    Jun 2006
    West Texas
    Hmm TEC-2104-3
    I figured since this is a vendor item they (Viconics) would not use an AO like JCI equipment. I don't need it to be writeable either. I have tried numerous ADI #'s with no success but I thought some of you guys may have come across this problem................rrh
    Taxachuesetts
    TEC-2104-3
    Never used that stat but sure looks like some dropped the ball. I would want the damper command and the minimum position setpoint. Call Viconics directly and see whats up, then press your JCI rep.
    How high did you map the ADI? The point list stops at 10. Try mapping up to 20.
    Nov 2005
    Shreveport, Louisiana
    Did you check your quicklit?
    UA Local 141
    Nov 2005
    Quote Originally Posted by beentheredonethat View Post
    What is your supervisory controller it is tied to? N30, pmi, NAE
    Is the point discovered?
    UA Local 141
    Jun 2006
    West Texas
    What is quicklit? I have 24-9890-455, Rev C literature. Supervisory device is FX40. I found the mixed air sensor as ADI-11.......................rrh
    Somewhere, WI
    Quicklit is a CD containing all of jci's docs on devices, same as on thier website:
    http://cgproducts.johnsoncontrols.co...px?main.aspx&2
    Nov 2005
    It has the information for the TEC and also information for the FX40..
    UA Local 141
    Jun 2006
    West Texas
    Thanks,,
    Yes to the quicklit question, the name didn't register. That's where I found the 24-9890-455 literature at. Not much info there except that the EC is 0-10 DC output. I'll send my request to the JCI boys and wait for a while. Thanks to everyone for your help............rrh
    Nov 2005
    Quote Originally Posted by ddcfreek View Post
    What is a prn?
    Is that what you use for a TEC were you do not direct map them but control them through a CS object.
    UA Local 141
    Somewhere, WI
    ".prn" file, it is a file that references point addresses to point names and descriptions for any N2 controller. Takes less time if you have the right one.
    Nov 2005
    Thank you sir
    UA Local 141