Have you checked all the multi-pin connections to the board and cleaned the connections on the board ?? Is the chiller located in a corrosive environment ?? ie paper mill etc ??
I have a trane RTWA125 that is displaying no communication,data not valid on the CLD I have checked cpm(1u1) board power,fuse and connections. a powerdown will reset it but it my work a couple of days before it displays it again. ANY INPUT
Thanks
If you fail to plan, you are planning to fail ("Coach Dave")
Hello I must be going. I cannot stay, I came to say , I must be going.(Jeffery T. Spauldlng)
Have you checked all the multi-pin connections to the board and cleaned the connections on the board ?? Is the chiller located in a corrosive environment ?? ie paper mill etc ??
The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
You bend em" I"ll mend em" !!!!!!!
I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
In the new big shop , greasin', oilin' . tweakin' n shinin' !!
from RLC-SVD03A-EN:
If the CLD Comm link to the CPM is broken, the message is:
No Communication, Data Not Valid
I hate comm problems, too.
good luck.
"Right" is not the same as "Wise".
Don't step on my favorite part of the Constitution just to point out your favorite part.
Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.
I replaced the 1u1 cpu board and the problem seems solved, and it is in a corrosive environment a tire plant.
Thanks for the input
If you fail to plan, you are planning to fail ("Coach Dave")
Hello I must be going. I cannot stay, I came to say , I must be going.(Jeffery T. Spauldlng)
You might want to try running a clean compressed air supply to the control panel and pressurize the control panel cabinet with clean air to prevent the corrosive atmosphere attacking the electronics . they do this a lot in paper mills etc and it does work .
The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
You bend em" I"ll mend em" !!!!!!!
I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
In the new big shop , greasin', oilin' . tweakin' n shinin' !!
you seal up the cabinet real well and provide compressed air through a regulator to maintain a positive pressure. the pressure needs to be quite a bit higher than you would think because the leakage is huge.
i have a liquid natural gas plant that does this to an old air cooled screw chiller. they use positve pressure to the control cabinet and a whole bunch of sensors and bells and whistles if something goes wrong. otherwise...could be a big-a-boom!!!
good luck.