    SNVT_press_p#US and an ilon100

    I'm trying to display a static pressure (SNVT_press_p#US) data point on an ilon100e3 and the value displays seven digits behind the decimal point. I'd like to reduce it to two. I'm using an ECP203 GFX and Lonwatcher. I can adjust the precision in the Distech Controls Browser and the value displays correct but not in the ilon.

    Thanks

  2. #2
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,129
    Another good argument for the Smart Server. This was always a problem with the e3. You can use some Javascript to trim the extra decimal places.

  3. #3
    Join Date
    Feb 2008
    Location
    Purcellville Va.
    Posts
    704
    You can use some Javascript to trim the extra decimal places.
    Let's just say I'm javascript illiterate, Can you give me a hint on how to get started?

    Thanks,
    Last edited by 381engineer; 11-28-2008 at 08:20 AM. Reason: Bad spelling.