    Hmm JCI's TE67NP Sensors

    Having a recurring problem with sensors reading excessively high causing over-cooling of space. At first I thought it was a bad sensor, so I replaced it but then it did it again about a month later. Several are doing the same thing. If I don't do anything to them they slowly drop to the actual room temp within a few hours. These have the RJ45 phone jack connectors. Has anyone experienced a similar problem?
    If I tell you how long I have been in this business, would it really matter?

  2. #2
    Join Date
    Nov 2008
    Location
    Rensselaer NY
    Posts
    2
    Post Likes
    I have cut off plug ends and crimped new ones both controller end and sensor end. loose connections equal high resistence which equals high temp.

  3. #3
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    the action described above is most likely you problem. The phone jack plugs get shorted together and cause hi temp readings. Positive temperature coefficient sensor.
    UA Local 141

  4. #4
    Join Date
    Sep 2003
    Posts
    161
    Post Likes
    Thread Starter
    I replaced the rj45 on the controller but not on the sensor. I'll do that on Monday, thanks.
    If I tell you how long I have been in this business, would it really matter?

  5. #5
    Join Date
    Sep 2003
    Posts
    161
    Post Likes
    Thread Starter
    That took care of it, thanks.
    If I tell you how long I have been in this business, would it really matter?

  6. #6
    Join Date
    Sep 2003
    Posts
    161
    Post Likes
    Thread Starter
    Is it unusual for the warm/cool adjust to be at -0.0?
    If I tell you how long I have been in this business, would it really matter?

  7. #7
    Join Date
    Jun 2005
    Posts
    286
    Post Likes
    There is an obscure problem few know about with platinum stats. I bed your stats are reading about 4 degree high. I do not remember part number for stats think yours is nickel so most likely the rj45. But if you or anyone else runs into it with platinum the fix is to set a -4 offset on the sensor in the controller. Their is a tech doc out there somewhere about it or was when I still worked at JCI

  8. #8
    Join Date
    Sep 2003
    Posts
    161
    Post Likes
    Thread Starter
    I noticed that and subtracted the offset. The warm cool adjust does change when manual setpoint is adjusted. Just seems odd.
    If I tell you how long I have been in this business, would it really matter?

  9. #9
    Join Date
    Sep 2006
    Location
    Anchorage Alaska
    Posts
    641
    Post Likes

    Setpoint

    On the Metasys PMI system sometimes the setpoints were in a control system and controlled by a GPL program with a master setpoint elsewhere in the system.
    Law Of The Thermostat: He who has the thermostat wins!!!!!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •