    Duct Sizing.

    I've been sizing duct systems for years. I go by feet per minute. For square duct I figure the supply at 650 FPM and on returns I figure 450. That's what I was taught in school. I'm working with some guys now that like to use the static pressure method. .08 to .1. This makes a big difference. 2000 CFM at 650 FPM gives you about a 20x25. 2000 CFM at .08 static gives you about 20x15. That a huge difference. What's the preferred method?

  2. #2
    Join Date
    Jul 2008
    Location
    Poestenkill, NY
    Posts
    769
    I size by friction loss, mostly.

    Velocity becomes more of a concern the closer you are to the register.

    If you sized all the returns in a commercial building to 450 fpm, the tinknocker would by you a beer, breakfast, lunch and dinner.

  3. #3
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,837
    I'll assume you're not really talking about the duct size but rather the face velocity of a supply or return appliance. The manufacturer's specs should be followed closely and it all depends on the noise factor as to how big the return will be. The grilled itself depends on the spacing of the louvers as they come anywhere from 3/8-in to 5/8-in. So the same size grille could give you two entirely different noise factors. If you're ducting a library or bedroom, you can't have the same noise you might have in a basketball court. All the man's specs I've seen deal with velocity, which is what you were taught to use, FPM. Static pressure needs to be factored into the total duct load but if it were me, I'd select the grilles based on FPM and noise and then take whatever static loss/drop that comes with it.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  4. #4
    Join Date
    Feb 2003
    Location
    pittsburgh,pa
    Posts
    727
    same here "friction loss" size ducts to accomadate blower that best fits the load.

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Quote Originally Posted by RefSupply View Post
    I've been sizing duct systems for years. I go by feet per minute. For square duct I figure the supply at 650 FPM and on returns I figure 450. That's what I was taught in school. I'm working with some guys now that like to use the static pressure method. .08 to .1. This makes a big difference. 2000 CFM at 650 FPM gives you about a 20x25. 2000 CFM at .08 static gives you about 20x15. That a huge difference. What's the preferred method?
    If they just use .08 or .1,without doing a Manual D to determine the actual friction Rate,then you are both wrong.Good news is your way is likely closer to being correct then their's.

    Your method will be larger ducts then needed at least some of the time,their's will be too small most of the time.

    Manual D from www.acca.org to learn more.

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,903
    If their just using .08 and .1, they are just using a rule of thumb.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Mar 2008
    Location
    Shelby Twp MI
    Posts
    820
    Most of the time when your dealing with commercial, you start with static. Reason being is the job is designed for a specific static rating. Most of the time 1" is standard, but, I've done jobs that spec'd 4" and 7".
    Jim

  8. #8
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    581
    Quote Originally Posted by RefSupply View Post
    I've been sizing duct systems for years. I go by feet per minute. For square duct I figure the supply at 650 FPM and on returns I figure 450. That's what I was taught in school. I'm working with some guys now that like to use the static pressure method. .08 to .1. This makes a big difference. 2000 CFM at 650 FPM gives you about a 20x25. 2000 CFM at .08 static gives you about 20x15. That a huge difference. What's the preferred method?
    I suspect the guys you are working with are using friction rate, not static pressure.

    0.08 or 0.1 are very low static pressure numbers and would require much larger ducts that 20x15 for 2000 CFM. However my program indicates that if you have a 20x15 duct at 0.08 friction rate then you get the 2000 CFMs, further suggesting to me they are using friction rates not static pressure to size the ducts.

    By the way, your 2000 CFM at 650 FPM using a 20 x 25 duct results in a friction rate of 0.02.....

    Key1
    In the land of the blind.....the man with one eye is king....

  9. #9
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    5,491
    There are several methods of duct sizing. Static regain, Velocity Reduction, Equal friction are three. Most people here seem to use the equal friction method.
    Like Beenthere said .1 or .08 are just thumbers.
    Tracers work both ways.