Results 1 to 13 of 13
    Nov 2008
    Johnson Controls
    Has anyone been dealing with Johnson Controls DX 9200 (using LON bus), NAE35? Would it be possible to get some information about Comm Pro and Metasys.
    Nov 2005
    You could start here.
    http://cgproducts.johnsoncontrols.co...opframe.aspx&0
    The DX9200 is junk.
    IlovemyjobIlovemyjobIlovemyjob....say it with me now!
    Nov 2008
    I need to have a connection between NAE and DX 9200 but I'm having some technical issues. Detecting DX automatically doesn't seem to work (in metasys environment). So, which should be the steps for getting connection. I have looked these materials on JCI's webpage but still I would appriciate some advice, some help to get started. Before I have used only N2 bus, programming with WGX and supervisioning with Supervison.
    Oct 2007
    Pa
    The LON bus on the DX-9200 never worked right. The VMA1200 sure but not the DX-9200.
    Nov 2008
    But if I were to use FX series controller with LON chip, would that be a better solution? Metasys itself should support DX but the problem is getting connection. I'm not sure, but If I have understood right, Comm pro should be used to preconfigure DX so it could be connected with NAE. I'm using Echalon LonTalk card but I can't get connected with that ether. DX LON-port has 3 connections- A, B and SHD and from cable for Ethalon has 4 wires- blue/blue-white, orange/orange-white. Right connection should be blue/blue-white to A and B?
    Have you got the connection between NAE and DX?
    Should I use Neuron ID or any other way to identify the controller?
    Which are right settings in Metasys for adding field device (if I'm trying to add it manually, I will have an error: "Inconsistant parameters")
    Do I have to configure DX before I try to connect it with NAE?
    Would it be easier with FX (I could test it with FX15)?
    Oct 2007
    Pa
    Is your LON card a PC-10 Type 2 PCMCIA Card? Have you had this card work correctly before?
    I personally would not recommend using FX LON, major problems. Do you have to use LON, or can you do N2?
    Nov 2008
    My LON card is PCC-10 and I have got it work before but using just WGX to upload LON points to DX (to get data from one DX to another). I have to use LON, before I used N2. It would help a lot if I could get connection between NAE and DX using LON.
    Nov 2005
    Shreveport, Louisiana
    Use the offline product literature link that is provided above and look up the NAE LON intergration and the DX9200 literature.
    UA Local 141
    Oct 2008
    Atlanta, GA
    Getting he LON side of NAE to work can be very difficult. You should be able to auto discover the DX though. It does have to be preconfigured to be detectable. The connections on the LON bus are not polarity specific as on the N2 it doesn't matter how you hook them up. What version of NAE do you have? if it is new I would expect 4.0.
    Nov 2008
    I'm using NAE35 with version 4.0 . How can I preconfigure DX? And what about NAE?
    Oct 2008
    Atlanta, GA
    You have to use the wgx software to configure the DX. It is standard on the system tools from Johnson. Another issue is with the NAE. At 4.0 they had a problem with the Lon integrations. It has a tendancy to not work. They released a patch to fix the problem but if you don't have the newest version of NAE you probably don't have the patch. Do you have access to any Johnson software? If so what do you have, do you have an ADS/ADX?
    Nov 2005
    DO you have LN Builder 3 software or some kind of LON maker type software?
    UA Local 141
    Nov 2008
    I managed to solve the problem with LON. Another questuin raised- do you know where could I get fx15 firmware update (.a37 file)?