LON API Migration to BACnet
I have an existing LON API
Circon system that I would like to get migrated over to a BACnet MS/TP (Metasys)
: system and use the same twisted pair.
I'll be replacing the existing LON controllers with BACnet. Can they reside on the same wire? What are the side effects?
-
11-13-2008, 12:40 PM #2
Permanently Removed
- Join Date
- May 2002
- Posts
- 9,564
Do you need to do much with it? Maybe you can slap on a Loytec LGATE and transfer those points over. I think you should also be able to get the CP values.
-
11-13-2008, 09:31 PM #3
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,254
You can not use the same wire for LON devices and BacNet devices. one or the other.