    Beer walkin problems....

    Brand new beer cooler, roughly 30' long, 8' wide and 10' high. I was called in because the low bid out of area contractor was clueless I guess. Woulldn't pull down below 42 degrees after several days. Both evaps frozen with 2" thick frost on the bottom third of the coil. I defrosted the coils to find the txv sensing bulbs coiled up all nice and pretty, the way they come out of the box. So, I strapped them on. Easy fix right? Wrong. SH had obviously never been set. So I hook up my YJ DRSA to see 35 degrees of SH at the suction outlet on both evaps. Hmmm. I ended up backing the txv's all the way out, never could get better than 26 deg SH at the evaps. To make things even more fun, the cond unit is on top of the cooler, and is now unaccessable.They built a lovely backbar to block the access. Sheesh. Pumped the system down using the stat to close the LL solenoid. Put in a sightglass and an access port on the liquid line so I could at least see a little of what was going on.Stuck the vac on to pull out as much air as possible.

    So here are the important numbers

    Climate control cond unit m/n HWN020
    Climate Control evaps (2) m/n LSC070AHK
    sporlan SQE 1(3/4)- vc txv with # 1 cartridge
    R-22 nozzle L-1/3
    sightglass shows full column of liquid
    suction 37.4 psig
    liquid line at 184 psig
    26 deg superheat

    It's the end of a 20 hour day, I'm fried and the only thing that I can think of is wrong nozzle.
    Planning to call Heatcraft in a couple of hours. Whadda you guys think?
    "The trouble with the world is the stupid are cocksure and the intelligent full of doubt" -Bertrand Russell

  2. #2
    Join Date
    Feb 2003
    Location
    NH & Cebu
    Posts
    1,614
    Post Likes
    Just did some real quick numbers. Gotta fly out the door in a sec. Your unit will do 14330 @ 20 degree evap. In URs catalog, an 8x30x8 box needs 14200-18000 btu. But I'm sure you have glass doors, which the chart doesn't take into account. Hmm...sure you have enough HP there?

    Maybe someone with a little more time can run the load

  3. #3
    Join Date
    Jun 2005
    Location
    Atlanta - Retired
    Posts
    1,250
    Post Likes
    coolerfixer,

    The equipment in this box is undersized. TXV's wide open, high superheat and high temperatures are the symptons.

    A typical 8 x 30 x 10 beer cooler requires about 25,462 btuhs. If it's a display cooler with glass doors, lets say 11, the btuh requirements is about 37,208 btuh.

    The equipment you have: HWN020 Climate unit, water cooled, pumps 16,760 btuhs at a +25 SST. This equates to a 11.7 TD matched with the 2 ea LSC070 evaps.

    You should have the customer call his low bidder or be prepared to buy more equipment from you.

  4. #4
    Join Date
    Dec 2005
    Location
    In the sticks,Northern Idaho
    Posts
    341
    Post Likes
    Thread Starter
    No display doors. Pretty much a tap room. to store kegs and bottle backstock. Very limited entry to add heat. Imperial Mfg made the box and sized the equipment. Spoke with them and they stand by their sizing. Talked to engineering this am. Thinking that maybe Mr. Lowbid charged with 404a instead of 22. Will be heading over to recover charge, evacuate and charge with fresh 22. I'll report back.
    "The trouble with the world is the stupid are cocksure and the intelligent full of doubt" -Bertrand Russell

  5. #5
    Join Date
    Jul 2007
    Location
    regina saskatchewan
    Posts
    257
    Post Likes
    What ambient temps at the condensor?
    Artificial Intelligence is no match for Natural Stupidity

  6. #6
    Join Date
    Dec 2005
    Location
    In the sticks,Northern Idaho
    Posts
    341
    Post Likes
    Thread Starter
    Quote Originally Posted by cretan View Post
    What ambient temps at the condensor?
    It's a closed loop cooling tower system feeding the water cooled condenser. Thus the 184 psig high side.
    "The trouble with the world is the stupid are cocksure and the intelligent full of doubt" -Bertrand Russell

  7. #7
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by coolerfixer View Post
    It's a closed loop cooling tower system feeding the water cooled condenser. Thus the 184 psig high side.
    How would one deduct that it was a cooling tower based on that?

    Do air cooled condensing units not also run at 184 psig?........Or am I missing something here?

    Cretan, I think that was a good question....keep askin' and keep learnin'
    "The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield

  8. #8
    Join Date
    Dec 2005
    Location
    In the sticks,Northern Idaho
    Posts
    341
    Post Likes
    Thread Starter
    Quote Originally Posted by markettech View Post
    How would one deduct that it was a cooling tower based on that?

    Do air cooled condensing units not also run at 184 psig?........Or am I missing something here?

    Cretan, I think that was a good question....keep askin' and keep learnin'

    Sorry, no malice intended, just a really tired brain. Anyway, pulled out the refrigerant (whatever it is) and in the process, I see flocking occuring in the sightglass in my manifold. Wonderful. So it probably is 404a reacting with the oil. So I stick the vacuum pump on for 2 hours knowing that I'm not gonna get all the gas out of the goo. Recharged with fresh R22, and BINGO, 12 degrees of SH on startup. It drops down to 10 deg SH when it nears the operating temp, BUT! The txv's are still backed all the way out. So I'm still not completely satisfied. I probably have a refrigerant cocktail now. I told the customer that I plan on pulling and replacing the charge again in a week in hopes of the flocking breaking down and releasing the remaining 404a. Box pulls down to 34 degrees no problem now, although I set it to 36 to be safe, no lite beer slushies please. Customer is happy. Oh, I measured the box too. 30' long x 6' wide x 8' high. Just a couple of feet off (chuckle).
    "The trouble with the world is the stupid are cocksure and the intelligent full of doubt" -Bertrand Russell

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •