    Cond/Mod Boiler air intake condensation problems?

    Has anyone ever had problems with the condensation from the intake getting the air pump wet and shorting it out?

    I have a Weil-Mclain Ultra 105 boiler and it seems like a design flaw having the intake flow right into the boiler to get all the compents wet?

    Why do they do this? Has anyone experienced any problems?

    Thanks for all the help this forum has provided me. <My installer hadn't ever done an Ultra boiler before mine. me=guinea pig

  2. #2
    Join Date
    Feb 2004
    Location
    Where is air is clean
    Posts
    13
    Post Likes
    Please don't say that I just put in a 155 unit. and it's getting cold here in NewYork

  3. #3
    Join Date
    Nov 2008
    Posts
    12
    Post Likes
    Thread Starter

    Weil-Mclain Ultra boilers

    Quote Originally Posted by newyorkart View Post
    Please don't say that I just put in a 155 unit. and it's getting cold here in NewYork

    Sorry, I read something about that late last night in another forum.

    It makes sense to me, I looked inside the cover of the Ultra and the intake is directly above the air pump and its electrical connections!

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Cold combustion air does not condensate on warm objects.

    If an Ultra is getting condensate from the combustion air, then you will find the exhaust termination is not not installed properly.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •