    Question Q : Trane Package Unit Test Mode

    Hello My name is Jay
    I'm a 21yr old working as an installer for a local hvac contractor
    In process of moving into servicing.
    I've been installing ducts, placing units, doing gas piping & etc for about 2 years right out of high school
    I haven't done many parts of the jobs that require me to mess around with wires(tstat wire, pan switch and low voltage wiring is probably all i have ever messed with)
    So my knowledge is not as its best.

    Could someone please explain to me how Trane Test Mode works?
    I saw some forums and installer's manual online but I can not understand
    the process by reading those Because I do not know the basics.

    If someone could explain thoroughly, and maybe even step by step,
    it will be greatly...greatly...greatly.. appreciated !

    thank you so much in advance,
    Jay

  2. #2
    Join Date
    Jan 2016
    Posts
    11
    Post Likes
    I'm assuming your talking Voyager,Precedent or odyssey lines. You simply jump out test1 and test2 on the LTB. If you leave your jumper on it will step through each step every 30 seconds. You can also step it through makes it a little faster. If you remove the jumper it will stay in that mode for 60 seconds except in defrost mode. I highly recommend you get a tech with more experience before woking on these units. Good luck!

  3. Likes jaych liked this post.
  4. #3
    Join Date
    Jan 2016
    Posts
    11
    Post Likes
    It will stay in the mode for 60 minutes if remove jumper not 60 seconds . My bad.

  5. #4
    Join Date
    Jan 2016
    Location
    N.J.
    Posts
    45
    Post Likes
    https://www.google.com/url?sa=t&rct=...11396085,d.dmo
    Read jay read it's the only way to become a great tech. pg 37
    note if you have a network card on the system you need to disable or test mode will not work

  6. Likes jaych liked this post.
  7. #5
    Join Date
    Jan 2016
    Posts
    5
    Post Likes
    Thread Starter
    Thanks
    but how do you know which mode you are in?
    and what do you exactly get from it?
    ones that i've see has test 1,2 24vac 1,2,3 and cpr-something 1,2,3, I think

    P.S. - Oh i'm not servicing any units yet lol
    just always been curious how that works

    Again thank you !

  8. #6
    Join Date
    Jan 2016
    Posts
    11
    Post Likes
    Test1 and test2 not 1 and 2 on LTB that's 24v. Test 1 and 2 is 5vdc circuit. Each mode has a resistance value that's different I can't remember what it is it should be labeled in unit. And one way of knowing what mode your in is by what the unit is doing.

  9. #7
    Join Date
    Jul 2012
    Location
    WA
    Posts
    3,250
    Post Likes
    The sticker on the electrical compartment cover panel lists the order of the test modes. It's useful because a lot of trane units aren't controlled by standard stats and you don't always have a R and W to jump to test the heat.

  10. #8
    Join Date
    Apr 2012
    Posts
    5
    Post Likes
    The sequence is as follows:
    Fan On
    Economizer open
    Cooling Stage 1
    Cooling Stage 2 (if present)
    Cooling stage 3 (if present)
    Heat Stage 1
    Heat Stage 2 (if present)

    Last step would be exiting test mode. Cycling power will also do the same.

    The LED on the RTRM board will begin to flash steady when in test mode with a single pule and will quite when out of test mode. The order of sequence stays the same the number of steps varies depending on how many cooling or heating stages you have. The number of stages above is example only.

    All safeties are still in play on test mode, so if you know you have two stages of cooling and second stage does not come on, then there is an issue with the circuit.

    On later models the OA sensor also came into play, so if it's cold outside you would need to warm it up if you are trying to bring on compressors for testing purposes.

  11. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    First, you need to quickly meet the requirements for Pro membership, and get your application in. Then, we can give you more detailed help in the Pro area.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  12. #10
    Join Date
    Apr 2016
    Location
    California
    Posts
    20
    Post Likes
    smack had it right on. But I think that after fan on, on some units there is an exhaust mode as well.

  13. #11
    Join Date
    Dec 2014
    Posts
    3,941
    Post Likes
    Also dehumidify.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •