Thread: Which method for preheating OA for make-up air unit?

  1. #1
    Join Date
    Jan 2016
    Posts
    11
    Post Likes

    Which method for preheating OA for make-up air unit?

    I have narrowed it down to two options for preheating the incoming OA for our MAU's in an existing system which currently pulls in 100% outside air but are unable to do so in the colder months due them being heat pumps. Usually they will trip out on a low temp fault and need to be reset.

    Option 1 - Add a mixing damper in the plenum after the OA damper and modulate that to mix more plenum air when the OA temps get colder.

    Option 2 - Add electric pre-heaters to condition the OA

    There are no exhaust systems integrated with these MAU's so a energy recovery wheel would not be an option.

    Any input or additional options appreciated.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,746
    Post Likes
    Why 100% OA?

    Generally with 100% OA there are no mixing dampers.

    Steam is my first choice, I've used HW but it a complicated control system for freeze protection.

  3. #3
    Join Date
    Jan 2016
    Posts
    11
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Why 100% OA?

    Generally with 100% OA there are no mixing dampers.

    Steam is my first choice, I've used HW but it a complicated control system for freeze protection.
    I believe when the building was first put up the mixing dampers may have been used and balanced and set to maintain static pressure. But this 40 years later and about 1/2 of the units have mixing dampers and the other that have been added on over the years do not. Steam is not an option as it is not in place.

  4. #4
    Join Date
    Jul 2007
    Location
    Delta BC Canada
    Posts
    140
    Post Likes
    Depending on how much CFM you require. Electric pre heating could get very expensive. Could you not use a Heat pump to pre heat the air with electric back up heat? Installing a small hydronic system to provide the necessary heat to temper the air.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,746
    Post Likes
    That would be one huge heat pump to maintain 50* Delta T then what do you do during defrost?

  6. #6
    Join Date
    Jul 2007
    Location
    Delta BC Canada
    Posts
    140
    Post Likes
    Yes pecmsg that could be a very large heat pump.The OP does not give much information as to CFM that is being supplied or what he has available for an energy source.He

    says an option is electric pre-heaters , Those are going to be some pretty big heating elements.

    There are definitely some cost efficient ways to pre heat the air but it sounds like his options are limited.

    Even a basic gas fired rooftop make up air has got to be more cost effective that a large KW duct heater.

  7. #7
    Join Date
    Feb 2014
    Posts
    29
    Post Likes
    What's the application? 100% Oa but no exhaust. What is "cold" where you are?

  8. #8
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    I've had good luck with direct fired nat gas section using modulation like Maxitrol.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  9. #9
    Join Date
    Jan 2016
    Posts
    11
    Post Likes
    Thread Starter
    Quote Originally Posted by DPinst View Post
    Yes pecmsg that could be a very large heat pump.The OP does not give much information as to CFM that is being supplied or what he has available for an energy source.He

    says an option is electric pre-heaters , Those are going to be some pretty big heating elements.

    There are definitely some cost efficient ways to pre heat the air but it sounds like his options are limited.

    Even a basic gas fired rooftop make up air has got to be more cost effective that a large KW duct heater.
    CFM ranges of the units range from 1200-2000. The few electric preheaters that were installed already range from 10-25kw with most not running at more than 50% on the coldest days or night which is around 0dF here.

    All we need to do realistically is preheat the air up to about 45dF which is the minimum rated intake air for the heat pump and then that can take over to reheat the air again.

    rooftops/gas fired is not an option here for multiple reasons.

    The purpose of these units is ventilation air for the population. These units blow into the plenum and the other units pull off of that to provide fresh air to the floor space.

    That's why my original thought of why there are mixing dampers on some of the original units. These could have been modulated at one point so that in the winter it would take in less OA and mix more plenum air effectively raising the intake temperature and not needing a preheater. The downfall is you bring in less outside air.

  10. #10
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    What kind of population and floor space needs all of that fresh air?

    I'm guessing a bit of engineering and re-ducting will have a short pay back then continue to pay nice dividends for a long while.


    Quote Originally Posted by Matt78 View Post
    CFM ranges of the units range from 1200-2000. The few electric preheaters that were installed already range from 10-25kw with most not running at more than 50% on the coldest days or night which is around 0dF here.

    All we need to do realistically is preheat the air up to about 45dF which is the minimum rated intake air for the heat pump and then that can take over to reheat the air again.

    rooftops/gas fired is not an option here for multiple reasons.

    The purpose of these units is ventilation air for the population. These units blow into the plenum and the other units pull off of that to provide fresh air to the floor space.

    That's why my original thought of why there are mixing dampers on some of the original units. These could have been modulated at one point so that in the winter it would take in less OA and mix more plenum air effectively raising the intake temperature and not needing a preheater. The downfall is you bring in less outside air.

  11. #11
    Join Date
    Jan 2016
    Posts
    11
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    What kind of population and floor space needs all of that fresh air?

    I'm guessing a bit of engineering and re-ducting will have a short pay back then continue to pay nice dividends for a long while.
    Ventilation and make-up air technically, these buildings are upwards of 450,000 sqft each. Using rooftops in the fashion i would want to would eliminate 20 heat pumps and replace them with 6 RTU's at one building, but this is not an option unfortunately.

  12. #12
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    If it's make up air, then you cannot restrict the 100% outside air.

    What is inside the building that needs all of that fresh air?


    Quote Originally Posted by Matt78 View Post
    Ventilation and make-up air technically, these buildings are upwards of 450,000 sqft each. Using rooftops in the fashion i would want to would eliminate 20 heat pumps and replace them with 6 RTU's at one building, but this is not an option unfortunately.

  13. #13
    Join Date
    Mar 2011
    Location
    Manchester NH
    Posts
    391
    Post Likes
    By the way you said "population" are you talking about a prison? Just curious


    Sent from my iPhone using Tapatalk

  14. #14
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    Yeah, I thought that too. The next thought was chickens.

    We still don't have a clue if all of that fresh air is required. Could've just been a low bid to replace a bunch of swamp coolers. And they didn't want to penetrate the roof for a return plenum.


    Quote Originally Posted by HVAC-matt View Post
    By the way you said "population" are you talking about a prison? Just curious


    Sent from my iPhone using Tapatalk

  15. #15
    Join Date
    Nov 2016
    Location
    Redmond, WA
    Posts
    1
    Post Likes
    "Transpired solar collectors" aka "solar ventilation pre-heaters" represent an option I've not seen in this discussion.

    Solarwall, the granddaddy of the technology is a choice but if accessing the lowest cost at the highest efficiency in this technology is desired I'd suggest looking at fabric transpired solar collectors especially if the application is for a rooftop installation. The geotextile collector was patented by the "National Renewable Energy Laboratories" but has been used mostly in the agri-sector where costs are much more acute than in commercial applications.

    If you want more info on this subject just ask

  16. #16
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    It seems someone already installed electric pre-heat successfully on other units that work, I would just go with that.


    Sent from my iPhone using Tapatalk

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •