    Something isn't right.

    49°F rise at 1000 CFM=52,920BTU output
    61.3°F rise at 1400 CFM=92,685BTU output.

    Your air flow may be much lower then what its set for.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    581
    Wraujr,

    If you post pictures of how your xv95 connects to your duct work you may be provided some insight on whether it looks overly restrictive.....ultimately static pressure measurement should provide some insight.