Estimating Cost to run heat pump vs. nat.
About how much would it cost to run a 10 seer hotel style heat pump instead of an 80% AFU natural gas F.A.U. with an electric blower?
California Electricity….. ~ $0.30 x Kwh
California Gas………….... ~ $1.63 x Therm or CCF
400 sq’ room w/ 2 un-insulated walls and 2 single pane windows.
Mild climate in Southern California near Disney Land. Almost never below 32*F
aprox 4 heating months
Thanks for advice.
-
11-06-2008, 02:13 PM #2
Regular Guest
- Join Date
- Jun 2007
- Location
- The Twilight Zone
- Posts
- 2,964
Not sure about the C.O.P. (Coefficient of Performance) range for a 10 SEER hotel style heat pump, but here's the math (plug in the right C.O.P. when you find it).
Compare the cost of 1 million btu's of heat.
Gas furnace with gas at $1.63 per therm, 80% efficient furnace:
(1,000,000 / 103,000 btu per therm) x 1.63 / .8
= $19.78
Heat pump with electricity at 30 cents per kw-hr (ouch!!), C.O.P. = 3? at 40F:
(1,000,000 / 3414 btu per kw-hr) x .3 / 3
= $29.29
In the above example, gas is 68% cheaper than the heat pump (if C.O.P. = 3 at 40F) for the same 1,000,000 btu's of heat.
Your gas price is reasonable. Your electric price is outrageous.
Good luck.
-
11-06-2008, 02:35 PM #3
Regular Guest
- Join Date
- Mar 2008
- Posts
- 74
Last edited by heater99; 11-06-2008 at 02:44 PM. Reason: more questions
-
11-06-2008, 02:52 PM #4
Regular Guest
- Join Date
- Jun 2007
- Location
- The Twilight Zone
- Posts
- 2,964
-
11-06-2008, 03:18 PM #5
Regular Guest
- Join Date
- Mar 2008
- Posts
- 74
Would you assume that that 10,000,000 BTU,s would cover a winter season?
Annual cost for gas ………….....= $197.80
Annual cost for Heat pump…..= $292.90
Difference…………….................= $105.00 per year.
Cost of installing through wall Heat pump ………...= ~$Removed
Cost of installing Gas F.A.U. + duct + gas line ….= ~$Removed
Difference………………..………………………...................= ~$Removed
Extra cost of Gas FAU …= $700
Energy savings …………..= $105
The heater will be financed.
Diff of $700 x 6% = about $40 a year
Add at least $15 a year to run the blower.
Assuming no change in utility rates they would break even in about 14 years.
Q1. Dose 10,000,000 BTU,s sound reasonable for a season?
Q2. Dose this look right?
No equipment pricing in posts pleaseLast edited by HeyBob; 11-06-2008 at 05:37 PM.
-
11-06-2008, 03:23 PM #6
Gas furnace at 80% efficiency=$20.38 for gas to deliver 1,000,000 BTUs.
If you include the heat from the blower motor, and the cost of electric for it.
It comes out to $29.53 for 1,000,000 BTUs of deliver heat from an 80% gas furnace.
A heat pump (at a COP of 3 ) with 3.5KW strip heat kit to temper the air during defrost, comes out to $29.29 to deliver 1,000,000 BTUs of heat, at temps requiring a defrost.
The question is, will the HP PTAC your looking at have a COP of 3?
-
11-06-2008, 03:27 PM #7
-
11-06-2008, 03:55 PM #8
-
11-06-2008, 04:18 PM #9
Professional Member*
- Join Date
- Jul 2008
- Location
- Poestenkill, NY
- Posts
- 764
Hotel Rooms have sporadic occupancy. If the room is actually often vacant with an aggressive set-back, the payback for gas would be sloooow. Different story if it's rented all teh time.
ALso, this has everything to do with climate - does it get cold enough to need back up resistance? That changes everything...
-
11-06-2008, 05:39 PM #10
-
11-07-2008, 02:03 AM #11
Regular Guest
- Join Date
- Mar 2008
- Posts
- 74
-
11-07-2008, 02:14 PM #12
Regular Guest
- Join Date
- Mar 2008
- Posts
- 74
Considering a Friedrich Twin Temp heat pump YS13L33
http://www.friedrich.com/products/Mo...?model=YS13L33
It is 11 EER.
A COP rating is not available according to Friedrich’s tec. Support
I don’t think more efficient PTAC’s are commercially available with a heat pump.
-