    TXV is hissing - what's that mean?

    Regular long-time customer calls and says that the walk-in box is making a hissing noise - inside the walk-in. It's been hissing for a few days. the hissing noise comes from the end of the evaporator where all the pipes connect he says. The box temperature is fine. The hissing continues for a little while if the evap fans are shut off. And he says that it didn't make the hissing noise before now.

    The sightglass is full.

    What would make a new hissing noise?

    Any ideas?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  2. #2
    Join Date
    Oct 2008
    Location
    florida
    Posts
    138
    Post Likes
    Is there a head master on the condensing unit?with the temperature change it could be bypassing the coil and a little low on charge,compressor runs warmer too i have found.

  3. #3
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is online now Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Thread Starter

    Let me explain:

    This is a frankenstein system with the wrong indoor condensing unit out on the roof, cond. fan cycling only, with the incorrect compressor installed on it, and cobbled to some mis-matched evap. coil with the wrong TXV.

    The hobo who created it thankfully died and they called me.

    5' by 6' 40 degree walk-in. Original issue: in hot weather, with a warm box, say; after a power failure, the high suction would start the compressor cycling on the O/L and that would never stop until you cooled the compressor externally.

    I approached it in steps: first I fixed all the elaks and installed the correct TXV and used a pressure limiting valve to limit the pull-down amps.

    That worked so I never went any further. I will do it all over properly when it fails but it's been years now. <g>

    PHM
    -------



    Quote Originally Posted by pelican View Post
    Is there a head master on the condensing unit? with the temperature change it could be bypassing the coil and a little low on charge, compressor runs warmer too i have found.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  4. #4
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    Who said the sight glass is "full"? The customer? If so its probally empty.

  5. #5
    Join Date
    Aug 2006
    Location
    SFL
    Posts
    81
    Post Likes
    Quote Originally Posted by kbghdg View Post
    Who said the sight glass is "full"? The customer? If so its probally empty.
    lol aint that the truth!

  6. #6
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is online now Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Thread Starter

    No; he knows what the look for - it's definitely full <g>

    I know from experience that this unit loses temperature badly when the sight glass is just slightly less than half full. <g>

    PHM
    -------


    Quote Originally Posted by kbghdg View Post
    Who said the sight glass is "full"? The customer? If so its probally empty.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  7. #7
    Join Date
    Oct 2008
    Location
    florida
    Posts
    138
    Post Likes
    sometimes you have to settle with what ya got wish we could make em all perefect

  8. #8
    Join Date
    Feb 2007
    Location
    Deep South
    Posts
    355
    Post Likes
    Have you checked the suction line heat exchanger if it has one? Sometimes a liquid to suction rupture can cause noise.

    Steve

  9. #9
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by steve wright View Post
    Have you checked the suction line heat exchanger if it has one? Sometimes a liquid to suction rupture can cause noise.

    Steve
    And a big ball of ice on the head of the pump

  10. #10
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is online now Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Thread Starter

    Easier to find the problem with patience <g>

    This time I found the roof so warm (black rubber) and pleasant that after I attached the gauges and temp probes I was just sitting there watching the clouds overhead and the young ladies parade around the bank on one side and the hospital on the other, when the 35W unit-bearing condenser fan found began to first emit an odd noise and then eventually stop turning. Right after that the head pressure went to over 400 and the compressor shut itself down.

    So I guess that was the "hissing noise" the customer was hearing. <g> What I had been hearing was the normal TXV sound.

    Weirdly; the condenser fan motor looked and felt fine. Turned smooth and free and had oil still in the wick. Even with no blade attached it would run for maybe twenty minutes in silence, then start making an off noise, and then stop turning. And even at that point the shaft was perfectly free. I have never seen that happen with those simple little motors before. 99% of the time they are stuck and only extremely rarely free turning but won't run. But this one was intermittant.

    And the 400 lb. liquid feed was making the TXV "hiss". <g>
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •